Answer:
The log-mean-temperature-difference is 24.03⁰C
Step-by-step explanation:
First we need to know if the heat exchanger is in parallel flow or counter-flow. However, counter flow arrangement is best used to recover heat.
L.M.T.D for counter flow is given as;
![L.M.T.D =\frac{(T_h_f_1 -T_c_f_2)-(T_h_f_2 -T_c_f_1)}{2.3log[\frac{T_h_f_1 -T_c_f_2}{T_h_f_2 -T_c_f_1}]}](https://tex.z-dn.net/?f=L.M.T.D%20%3D%5Cfrac%7B%28T_h_f_1%20-T_c_f_2%29-%28T_h_f_2%20-T_c_f_1%29%7D%7B2.3log%5B%5Cfrac%7BT_h_f_1%20-T_c_f_2%7D%7BT_h_f_2%20-T_c_f_1%7D%5D%7D)
where;
Thf₁ is the initial temperature of the hot fluid = 80°C
Tcf₂ is the final temperature of the cold fluid = 51.5°C
Thf₁ - Tcf₂ = 80 - 51.5 = 28.5⁰C
Thf₂ is the final temperature of the hot fluid = 30°C
Tcf₁ is the initial temperature of the cold fluid = 10°C
Thf₂ - Tcf₁ = 30 - 10 = 20⁰C
![L.M.T.D = \frac{28.5 -20}{2.3Log[\frac{28.5}{20}]} \\\\L.M.T.D = \frac{8.5}{0.3538} =24.03^oC](https://tex.z-dn.net/?f=L.M.T.D%20%3D%20%5Cfrac%7B28.5%20-20%7D%7B2.3Log%5B%5Cfrac%7B28.5%7D%7B20%7D%5D%7D%20%5C%5C%5C%5CL.M.T.D%20%3D%20%5Cfrac%7B8.5%7D%7B0.3538%7D%20%3D24.03%5EoC)
Therefore, the log-mean-temperature-difference is 24.03⁰C
Answer:
c = -25
Step-by-step explanation:
First, simplify the constants on the left side of the equation
-2c-6-9=35
-2c-15=35, Add 15 to both sides
-2c-15+(15) = 35+(15)
-2c=50 Now, divide both sides by -2 to isolate the variable c
-2c/(-2) = 50/(-2)
c = -25 And here is the answer.
Answer:
40000
Step-by-step explanation:
Use force calculator
Answer:
A: 1.95 Two Decimal places.
B: 9.6 One Decimal place.
C: 81 No Decimal Places.
D: 44.53 Two Decimal Places.
E: 72.2 One Decimal Place.
Mark Brainliest Please to help me get to the next Rank!
#RoadToVituoso!
If you have the calculator TI-84. press 2nd sin(56.3 divided by 80.2)=44.58728408 you must round the number because sometimes they ask to round the number. (don't forget to pre 2nd before you press sin)