A three-phase wye-connected synchronous generator supplies a network through a transmission line. The network can absorb or deli

ver power while maintaining its terminal voltage constant. The four-pole, 60 Hz generator data rating are 40 MVA and 26 kV with a 0.85 p.u. reactance. The field current of the generator can be adjusted to regulate the excitation (induced) voltage from 0.75 to 1.5 times the rated voltage. The network voltage rating is 24 kV. The transmission line impedance and length are 0.07+j0.5 Ω/mi and 8 mi.
Calculate the generator induced voltage versus power factor, if the network voltage is at the rated value, and the bus absorbs the generator rated power. After this, plot the voltage regulation of the system versus the power factor. Use the induced voltage and network voltage for plotting the voltage regulation. The leading power factor varies from 0.5 to 1. What power factor corresponds to 10% regulation?

Engineering
1 answer:
Amanda [17]4 years ago
8 0

Answer:

the graph and the answer can be found in the explanation section

Explanation:

Given:

Network rated voltage = 24 kV

Impedance of network = 0.07 + j0.5 Ω/mi, 8 mi

Rn = 0.07 * 8 = 0.56 Ω

Xn = 0.5 * 8 = 4 Ω

If the alternator terminal voltage is equal to network rated voltage will have

Vt = 24 kV/√3 = 13.85 kV/phase

The alternative current is

I_{a} =\frac{40x10^{6} }{\sqrt{3}*24x10^{3}  } =926.2A

X_{s} =0.85\frac{13.85}{926.2} =12.7ohm

The impedance Zn is

\sqrt{0.56^{2}+4^{2}  } =4.03ohm

The voltage drop is

I_{a} *Z_{n} =926.2*4.03=3732.58V

r_{dc} =\frac{voltage}{2*current} =\frac{13.85}{2*926.2} =7.476ohm

rac = 1.2rdc = 1.2 * 7.476 = 8.97 Ω

The effective armature resistance is

Z_{s} =\sqrt{R_{a}^{2}+X_{s}^{2}    } =\sqrt{8.97^{2}+12.7^{2}  } =15.55ohm

The induced voltage for leading power factor is

E_{F} ^{2} =OB^{2} +(BC-CD)^{2}

if cosθ = 0.5

E_{F} =\sqrt{(13850*0.5)^{2}+(\frac{3741}{2}-926.2*12.7)^{2}   } =11937.51V

if cosθ= 0.6

EF = 12790.8 V

if cosθ = 0.7

EF = 13731.05 V

if cosθ = 0.8

EF = 14741.6 V

if cosθ = 0.9

EF = 15809.02 V

if cosθ = 1

EF = 13975.6 V

The voltage regulation is

\frac{E_{F}-V_{t}  }{V_{t} } *100

For each value:

if cosθ = 0.5

voltage regulation = -13.8%

if cosθ = 0.6

voltage regulation = -7.6%

if cosθ = 0.7

voltage regulation = -0.85%

if cosθ = 0.8

voltage regulation = 6.4%

if cosθ = 0.9

voltage regulation = 14%

if cosθ = 1

voltage regulation = 0.9%

the graph is shown in the attached image

for 10% of regulation the power factor is 0.81

You might be interested in
A treatment plant being designed for Cynusoidal City requires an equalization basin to even out flow and BOD variations. The ave
sineoko [7]

Answer:

The size of equalization basin is 6105.6 m³

Explanation:

The average flow is:

flow = ∑flow/n = 9.788/24 = 0.408 m³/s

Where n is the number or observations.

The inflow volume is:

V_{inflow} =Q*t

where t is the time interval

V_{inflow} =0.446(1*3600)=1605m^{3}

in the same way it is calculated the inflow volume for each observation

The outflow volume is:

V_{out} =Q_{out} *t=0.4*(1*3600)=1400m^{3}

The volume of flow is:

ds=V_{inflow} -V_{out} =1605-1400=205m^{3}

in the same way it is calculated the volume of flow for each observation. According to the file attach, the highest volume is 6105.6 m³

Download pdf
6 0
4 years ago
An ideal neon sign transformer provides 9130 V at 51.0 mA with an input voltage of 240 V. Calculate the transformer's input powe
BaLLatris [955]

Answer:

Input power = 465.63 W

current = 1.94 A

Explanation:

we have the following data to answer this question

V = 9130

i = 0.051

the input power = VI

I = 51.0 mA = 0.051

= 9130 * 0.051

= 465.63 watts

the current = 465.63/240

= 1.94A

therefore the input power is 465.63 wwatts

while the current is 1.94A

the input power is the same thing as the output power.

4 0
3 years ago
Given V1 = 8 vpp, R1 = 6 kΩ, V2 = 5 vpp, R2 = 3 kΩ, V3 = 10 vpp, R3 = 3 kΩ, and Rf = 14 kΩ, find Vout. Vout = vpp. (Round your a
iragen [17]

Answer:

Vout= 93.3V

Explanation:

For this question, consider circuit in the attachment 1.

This is the circuit of an inverting amplifier. In an inverting amplifier

Vout/Vin= -Rf/Rin

To calculate the Vout, we must find Rin and Vin. For this we must solve the input circuit (attachment 2)  using  Thevinine theorem. Thevnine theorem states that all voltage sources in a circuit can be replaced by an equivalent voltage source Veq and and all resistances can be replaced by an equivalent resistance Req. To find out Req all voltage sources must be short circuited (attachment 3)

1/Req= 1/R1+1/R2+1/R3

1/Req=1/6+1/3+1/3

Req=6/5

To find out Veq consider circuit in attachment 4. We will solve this circuit using nodal analysis. In nodal analysis, we use the concept that sum of currents entering a node is equal to the sum of currents leaving a node. So,

I1= I2+I3

(10-Veq)/6= (Veq-5)/3+(Veq-10)/3

Veq=8V

Now the input circuit can be simplified as shown in attachment 5. Solve for Vout using equation

Vout/Veq= -Rf/Req

Vout/8= -14/(6/5)

Vout= - 93.3

It is at an angle of 180° from Veq

7 0
3 years ago
Ground effect is felt at a height that is equal to the plane's wingspan.<br> True or False
Oliga [24]

Answer:

True

Explanation:

7 0
3 years ago
Describe two components of the MEDC mechanized agricultural system that may lead to an increase in water stress
Zina [86]

Mechanized agriculture refers to agricultural machinery capable of facilitating and enhancing agriculture. Mechanized agriculture does not require moving the soils and therefore is hard for water to enter into it.

<h3>What is mechanized agriculture?</h3>

Mechanized agriculture refers to the use of different technologies (e.g., precision agriculture GPs) in order to increase farmworker productivity.

Mechanized agriculture is a common practice in developed countries (MEDCs), whereas this practice is relatively uncommon in developing countries (LEDCs).

The techniques of mechanized agriculture do not require moving the soils and therefore is hard for water to enter into it.

Learn more about mechanized agriculture here:

brainly.com/question/1543791

8 0
3 years ago
Other questions:
  • Identify the types of bonding that occur within a polymer system and how this affects its properties
    9·1 answer
  • Write an ALP to separate odd and even numbers from an array of N numbers; arrange odd
    13·1 answer
  • An air conditioner is designed to bring 10,000 ft3/min of outside air (90°F, 29.8 inches Hg, 88% relative humidity) to 40°F, the
    9·1 answer
  • std::string x[n]; int mode1count = 0; // msft int mode2count = 0; // appl int mode3count = 0; // csco int mode4count = 0; // imb
    13·1 answer
  • HELP PLS<br> Is a book a solid, frame, shell or combination and WHY
    6·2 answers
  • Which option identifies the next step Kristin should take to test the design in the following scenario?
    6·1 answer
  • Determining criteria and constraints is part of which steps in the engineering design phase? doing an analysis researching the p
    10·2 answers
  • What is the function rule for the line? f(x)=−32x−2f(x)=−23x−2f(x)=32x−2f(x)=−32x+2A coordinate grid with x and y axis ranging f
    6·1 answer
  • How much horse power does a Lamborghini have
    6·2 answers
  • What line separates two lanes traveling in the same direction
    5·2 answers
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!