Answer:
Explanation:
This will be possible when setting them up in summer with a certain quantity of sag, they have already know that the cables won't be able to sag any further because of the heat. During winter, when the cables contract because of the cold weather, the sag will therefore be reduced, but much tension will not be put on the cables.
Answer:
The ground-fault circuit interrupter, or GFCI, is a fast-acting circuit breaker designed to shut off electric power in the event of a ground-fault within as little as 1/40 of a second.
Explanation:
Answer:
Z = 29.938Ω ∠22.04°
I = 2.494A
Explanation:
Impedance Z is defined as the total opposition to the flow of current in an AC circuit. In an R-L-C AC circuit, Impedance is expressed as shown:
Z² = R²+(Xl-Xc)²
Z = √R²+(Xl-Xc)²
R is the resistance = 4Ω
Xl is the inductive reactance = ωL
Xc is the capacitive reactance =
1/ωc
Given C = 12 μF, L = 6 mH and ω = 2000 rad/sec
Xl = 2000×6×10^-3
Xl = 12Ω
Xc = 1/2000×12×10^-6
Xc = 1/24000×10^-6
Xc = 1/0.024
Xc = 41.67Ω
Z = √4²+(12-41.67)²
Z = √16+880.31
Z = √896.31
Z = 29.938Ω (to 3dp)
θ = tan^-1(Xl-Xc)/R
θ = tan^-1(12-41.67)/12
θ = tan^-1(-29.67)/12
θ = tan^-1 -2.47
θ = -67.96°
θ = 90-67.96
θ = 22.04° (to 2dp)
To determine the current, we will use the relationship
V = IZ
I =V/Z
Given V = 12V
I = 29.93/12
I = 2.494A (3dp)
Answer:
The resultant moment is 477.84 N·m
Explanation:
We note that the resultant moment is given by the moment about a given point
The length of the sides of the formed triangles are;
l = sin(40°) × 4/sin(110°) ≈ 2.736
Taking the moment about the lower left hand corner of the figure, with the convention that clockwise moments are positive, we have;
The resultant moment, ∑m, is given as follow;
∑M = 250 N × 4 m + 400 N × cos(40°) × 4 m - 400 N × cos(40°) × 2 m + 400 N × sin(40°) × 2 m × tan(40°) - 600 N × cos(40°) × 2 m - 600 N× sin(40°) × 2 m × tan(40°) = 477.837084 N·m
Therefore, the resultant moment, ∑m ≈ 477.84 N·m clockwise.