A 650-kN column load is supported on a 1.5 m square, 0.5 m deep spread footing. The soil below is a well-graded, normally consol

idated sand with 훾 = 18.0 kN/m3 and the following SPT N60 values:
Engineering
1 answer:
insens350 [35]3 years ago
6 0

<u>Explanation:</u>

Determine the weight of footing

W_{f}=\gamma(L)(B)(D)

Where W_{f} is the weight of footing, γ is the unit weight of concrete,  L is the length of footing is the width of footing, and D is the depth of footing

Substitute 2 m \text { for } L, 1.5 m \text { for } B, 0.5 m \text { for } D \text { and } 23.6 kN / m ^{3} for γ in the equation

\begin{aligned}W_{f} &=\left(23.6 kN / m ^{3}\right)(2 m )(1.5 m )(0.5 m ) \\&=35.4 kN\end{aligned}

Therefore, the weight of the footing is 35.4 kN

Determine the initial vertical effective stress.

\sigma_{z p}^{\prime}=\gamma(D+B)-u

Here,   \sigma_{z^{p}}^{\prime} is initial vertical stress at a depth below ground surface  γ is the unit weight of soil, D is depth and u is pore water pressure.

Substitute 18 kN / m ^{3} \text { for } \gamma, 1.5 m \text { for } B, 0.5 m \text { for } D \text { and } 0 for u in the equation

\begin{aligned}\sigma_{z p}^{\prime} &=\left(18 kN / m ^{3}\right)(1.5+0.5) m -0 \\&=36 kPa\end{aligned}

Therefore, the initial vertical stress is 36 kPa

Determine the vertical effective stress.

\sigma_{z D}^{\prime}=\gamma D

Here,   \sigma_{z^{p}}^{\prime} is initial vertical stress at a depth below ground surface  γ is the unit weight of soil, D is depth and u is pore water pressure.

Substitute \(18 kN / m ^{3}\) for \(\gamma, 0.5 m\) for \(D\) and 0 for \(u\) in the equation.

\begin{aligned}\sigma_{z b}^{\prime} &=\left(18 kN / m ^{3}\right)(0.5 m )-0 \\&=9 kPa\end{aligned}

Therefore, the vertical stress at a depth below the ground surface is

9 kPa

Determine the influence factor at the midpoint of soil layer,

I_{e p}=0.5+0.1 \sqrt{\frac{q-\sigma_{s 0}^{\prime}}{\sigma_{z p}^{\prime}}}

Here I_{e p} is the influence factor at the midpoint of soil layer  \sigma_{z^{p}}^{\prime} is initial vertical stress, \sigma_{z^{p}}^{\prime} is vertical effective stress, and Q is bearing pressure

Substitute 36 kPa for \(\sigma_{z p}^{\prime}, 228.47\) kPa for \(q,\) and 9 kPa for \(\sigma_{z D}^{\prime}\) in the equation\begin{aligned}I_{\epsilon P} &=0.5+0.1 \sqrt{\frac{228.47 kPa -9 kPa }{36 kPa }} \\&=0.75\end{aligned}

Therefore the influence factor at the midpoint of the soil layer is 0.693

You might be interested in
Four of the minterms of the completely specified function f(a, b, c, d) are m0, m1, m4, and m5.
Sveta_85 [38]

Complete Question

The complete question is shown on the first uploaded image

Answer:

a) The required additional minterms  for f so that f has eight primary implicants with two literals and no other prime implicant are m_{2},m_{3},m_{7},m_{8},m_{11},m_{12},m_{13},m_{14} and m_{15}

b) The essential prime implicant are c' d',a'b',ab and cd

c) The minimum sum-of-product expression for f are

                  a'b' +ab +c'd'+cd+a'c',\\ a'b'+ab+c'd'+cd+a'd,\\a'b'+ab+c'd'+cd+bc'  and  \\ a'b'+ab+c'd' +cd+bd

Explanation:

The explanation is shown on the second third and fourth image

8 0
3 years ago
X cotx expansion using maclaurins theorem.
Lemur [1.5K]

It is to be noted that it is impossible to find the Maclaurin Expansion for F(x) = cotx.

<h3>What is Maclaurin Expansion?</h3>

The Maclaurin Expansion is a Taylor series that has been expanded around the reference point zero and has the formula f(x)=f(0)+f′. (0) 1! x+f″ (0) 2! x2+⋯+f[n](0)n!

<h3>What is the explanation for the above?</h3>

as indicated above, the Maclaurin infinite series expansion is given as:

F(x)=f(0)+f′. (0) 1! x+f″ (0) 2! x2+⋯+f[n](0)n!

If F(0) = Cot 0

F(0) = ∝ = 1/0

This is not definitive,

Hence, it is impossible to find the Maclaurin infinite series expansion for F(x) = cotx.

Learn more about Maclaurin Expansion at;
brainly.com/question/7846182
#SPJ1

4 0
1 year ago
Design circuits that demonstrate all of the principles listed below. Set up the circuits and take measurements to show that the
Nata [24]

<u>Explanation</u>:

For series

\Delta V=V_{1}+V_{2}+\ldots+V_{n}=I R_{1}+I R_{2}+\ldots+I R_{n}(\text {voltages add to the batter } y)

\(I=I_{1}=I_{2}=I_{n}\) (current is the same)

V=I R(\text {voltage is directly proportional to } R)

R_{e q}=R_{1}+R_{2}+\ldots+R_{n} \quad \text { (resistance increase) }

For parallel

\Delta V=\Delta V_{1}=\Delta V_{2}=\Delta V_{n} \quad(\text { same voltage })

I=I_{1}+I_{2}+\ldots+I_{n}(\text {current adds})

\(I=\frac{\Delta V}{R_{e q}} \quad(R \text { inversal } y \text { proportional to } I)\)

\frac{1}{R_{e q}}=\frac{1}{R_{1}}+\frac{1}{R_{2}}+\ldots+\frac{1}{R_{n}}

3 0
3 years ago
Determine the general lighting load for a two-story office building that measures 125 feet by 150 feet.
Irina-Kira [14]

The general lighting load for a two-story office building that measures 125 feet by 150 feet is 112, 500 sq ft.

<h3>What is lighting load?</h3>

Lighting loads are the energy used to power electric lights and they make up nearly a third of US commercial building energy use.

Lighting load = n(LW)

where;

  • L is length of the building
  • W is width of the building
  • n is number of story building

For one story building, = 3

For two story building, n = 6

Lighting load = 6 x 125 x 150 = 112, 500 sq ft.

Learn more about lighting load here: brainly.com/question/14070748

#SPJ12

7 0
1 year ago
NO LINK plsssss just answer
solmaris [256]

Answer:

Explanation:

4 0
2 years ago
Other questions:
  • What might cause a shotgun to explode?
    6·2 answers
  • Discuss four (4) advantages of direct and indirect water supply system.
    5·2 answers
  • A cooling system load is 96,000 BTUh sensible. How much chilled air is required to satisfy the load if the system is designed fo
    12·1 answer
  • For a fluid with a Prandtl Number of 1000.0, the hydrodynamic layer is thinner than the thermal boundary layers. a) True b) Fals
    5·1 answer
  • A nozzle receives an ideal gas flow with a velocity of 25 m/s, and the exit at 100 kPa, 300 K velocity is 250 m/s. Determine the
    14·1 answer
  • Please help me in this assignment.
    13·1 answer
  • On July 23, 1983, Air Canada Flight 143 required 22,300 kg of jet fuel to fly from Montreal to Edmonton. The density of jet fuel
    8·1 answer
  • When mass is the same, what is the relationship between radius and compression strength?
    5·1 answer
  • Ferroconcrete is reinforced concrete that combines concrete and ________. A. Lead c. Copper b. Iron d. Aluminum.
    6·1 answer
  • A fully charged new battery will have a low conductance reading.