12.50 An air conditioner operating at steady state takes in moist air at 28°C, 1 bar, and 70% relative humidity. The moist air f

irst passes over a cooling coil in the dehumidifier unit and some water vapor is condensed. The rate of heat transfer between the moist air and the cooling coil is 11 tons. Saturated moist air and condensate streams exit the dehumidifier unit at the same temperature. The moist air then passes through a heating unit, exiting at 24°C, 1 bar, and 40% relative humidity. Neglecting kinetic and potential energy effects, determine a. the temperature of the moist air exiting the dehumidifier unit, in °C. b. the volumetric flow rate of the air entering the air conditioner, in m3/min. c. the rate water is condensed, in kg/min. d. the rate of heat transfer to the air passing through the heating unit, in kW.

Engineering
1 answer:
Mandarinka [93]3 years ago
8 0

Answer:

Hey smith please see attachments for answer:

Please rate me good.

The attachments will provide you a detailed answer

Explanation:

You might be interested in
The steam requirements of a manufacturing facility are being met by a boiler whose rated heat input is 5.5 x 106 Btu/h. The comb
Veronika [31]

Answer:

Explanation:uhhhhhh all?

7 0
3 years ago
Refrigerant-134a at 700 kPa, 70°C, and 7.2 kg/min is cooled by water in a condenser until it exists as a saturated liquid at the
alex41 [277]

Answer:

The mass flow rate of cooling water required to cool the refrigerant is 123.788\,\frac{kg}{min}.

Explanation:

A condenser is a heat exchanger used to cool working fluid (Refrigerant 134a) at the expense of cooling fluid (water), which works usually at steady state. Let suppose that there is no heat interactions between condenser and surroundings.The condenser is modelled after the First Law of Thermodynamics, which states:

\dot Q_{ref} - \dot Q_{w} = 0

\dot Q_{ref} = \dot Q_{w}

\dot m_{ref}\cdot (h_{ref, in} - h_{ref,out}) = \dot m_{w}\cdot (h_{w, out} - h_{w,in})

The mass flow rate of the cooling water is now cleared:

\dot m_{w} = \dot m_{ref }\cdot \frac{h_{ref,in}-h_{ref,out}}{h_{w,out}-h_{w,in}}

Given that h_{ref,in} = 808.34\,\frac{kJ}{kg}, h_{ref, out} = 88.82\,\frac{kJ}{kg}, h_{w,out} = 104.83\,\frac{kJ}{kg} and h_{w,in} = 62.98\,\frac{kJ}{kg}, the mass flow of the cooling water is:

\dot m_{w} = \left(7.2\,\frac{kg}{min} \right)\cdot \left(\frac{808.34\,\frac{kJ}{kg}-88.82\,\frac{kJ}{kg} }{104.83\,\frac{kJ}{kg}-62.98\,\frac{kJ}{kg} } \right)

\dot m_{w} = 123.788\,\frac{kg}{min}

The mass flow rate of cooling water required to cool the refrigerant is 123.788\,\frac{kg}{min}.

4 0
3 years ago
(Specific weight) A 1-ft-diameter cylindrical tank that is 5 ft long weighs 125 lb and is filled with a liquid having a specific
lina2011 [118]

Answer:

The answer to the question is 514.17 lbf

Explanation:

Volume of cylindrical tank = πr²h = 3.92699 ft³

Weight of tank = 125 lb

Specific weight of content = 66.4 lb/ft³

Mass of content =  66.4×3.92699 = 260.752 lb

Total mass = 260.752 + 125 = 385.75 lb = 174.97 kg

=Weight = mass * acceleration = 174.97 *9.81 = 1716.497 N

To have an acceleration of 10.7 ft/s² = 3.261 m/s²

we have F = m*a = 174.97*(9.81+3.261) = 2287.15 N = 514.17 lbf

5 0
3 years ago
• ¿Qué les reclamó Dios al pueblo?<br> • ¿Qué consecuencias hubo?
HACTEHA [7]

a quien alos israelitas

8 0
3 years ago
Refrigerant-134a enters the coils of the evaporator of a refrigeration system as a saturated liquid–vapor mixture at a pressure
Klio2033 [76]

Answer:

A) ΔS_refrigerant = 0.70754 Kj/K

B) ΔS_space = -0.68441 Kj/K

C) ΔS_total = 0.02313 Kj/K

Explanation:

A) From he table attached, at Pressure of 140 KPa, and by interpolation, we get, Temperature of T = -18.77°C

Converting to degree kelvin yields;

T = -18.77 + 273 = 255.23 K

Formula for entropy change of refrigerant is given as;

ΔS_refrigerant = Q_in/T_refrigerant

We are given Q = 180 KJ

Thus, ΔS_refrigerant = 180/255.23 = 0.70754 Kj/K

B) Formula for entropy change of cooled space is given as;

ΔS_space = Q_out/T_s pace

T_space = -10°C = 273 - 10 = 263K

Thus, ΔS_space = -180/263 = -0.68441 Kj/K

C) the total entropy change would be;

ΔS_total = ΔS_refrigerant + ΔS_space

Thus,

ΔS_total = 0.70754 - 0.68441 = 0.02313 Kj/K

8 0
3 years ago
Other questions:
  • 6.15. In an attempt to conserve water and to be awarded LEED (Leadership in Energy and Environmental Design) certification, a 20
    14·1 answer
  • To unload a bound stack of plywood from a truck, the driver first tilts the bed of the truck and then accelerates from rest. Kno
    7·1 answer
  • When circuit switching is used, what is the maximum number of circuit-switched users that can be supported? Explain your answer
    6·1 answer
  • Using the results of the Arrhenius analysis (Ea=93.1kJ/molEa=93.1kJ/mol and A=4.36×1011M⋅s−1A=4.36×1011M⋅s−1), predict the rate
    10·1 answer
  • A thick spherical pressure vessel of inner radius 150 mm is subjected to maximum an internal pressure of 80 MPa. Calculate its w
    9·1 answer
  • (a) In a 3-phase, 4-wire system, the currents are in the A, B, and C lines under abnormal conditions of loading were as follows:
    9·1 answer
  • Multilane roads use what to divide lanes of traffic moving in the same direction.
    14·2 answers
  • Engineered lumber should not be used for
    15·1 answer
  • What type of cartilage provides support and shock absorption?.
    13·1 answer
  • A compound sliding miter saw can be used to make
    5·1 answer
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!