Answer:
A) 282.34 - j 12.08 Ω
B) 0.0266 + j 0.621 / unit
C)
A = 0.812 < 1.09° per unit
B = 164.6 < 85.42°Ω
C = 2.061 * 10^-3 < 90.32° s
D = 0.812 < 1.09° per unit
Explanation:
Given data :
Z ( impedance ) = 0.03 i + j 0.35 Ω/km
positive sequence shunt admittance ( Y ) = j4.4*10^-6 S/km
A) calculate Zc
Zc =
=
=
= 282.6 < -2.45°
hence Zc = 282.34 - j 12.08 Ω
B) Calculate gl
gl =
d = 500
z = 0.03 i + j 0.35
y = j4.4*10^-6 S/km
gl = 
= 
= 0.622 < 87.55 °
gl = 0.0266 + j 0.621 / unit
C) exact ABCD parameters for this line
A = cos h (gl) . per unit = 0.812 < 1.09° per unit ( as calculated )
B = Zc sin h (gl) Ω = 164.6 < 85.42°Ω ( as calculated )
C = 1/Zc sin h (gl) s = 2.061 * 10^-3 < 90.32° s ( as calculated )
D = cos h (gl) . per unit = 0.812 < 1.09° per unit ( as calculated )
where : cos h (gl) = 
sin h (gl) = 
Answer with Explanation:
Part a)
The volume of water in the tank as a function of time is plotted in the below attached figure.
The vertical intercept of the graph is 46.
Part b)
The vertical intercept represents the volume of water that is initially present in the tank before draining begins.
Part c)
To find the time required to completely drain the tank we calculate the volume of the water in the tank to zero.

Part d)
The horizontal intercept represents the time it takes to empty the tank which as calculated above is 13.143 minutes.
Hi
Acetylene and propane
I hope this help you!
Answer:

Explanation:
From the question we are told that:
Water flow Rate 
Initial Temperature 
Final Temperature 
Let
Specific heat of water 
And


Generally the equation for Heat transfer rate of water
is mathematically given by
Heat transfer rate to water= mass flow rate* specific heat* change in temperature



Therefore