what is it ill know your question??!!
Answer:
The power is 
Explanation:
In order to obtain the power it consumes we need to first obtain the resistance of the hair dryer at 120 V

Now the power supplied in Europe at their voltage of 230V would be

Looking the power obtain we see that it is higher than 1530 W so this would cause the dryer to smoke.
Answer:
Check the explanation
Explanation:
Let’s take for instance, when an object with a mass of 10 kg (m = 10 kg) is moving at a 5 meters per second (v = 5 m/s) velocity rate, the kinetic energy is equal to 125 Joules
Kindly check the attached images below to get the step by step explanation to the question above.
Based on the National Electrical Code (NEC), a 450-Ampere fuse should be used to protect this polyphase (three-phase) squirrel cage inductor motor.
<u>Given the following data:</u>
- Power rating = 100-horsepower.
<h3>How to determine the correct fuse rating?</h3>
According to Table 430.52 of the National Electrical Code (NEC), a dual-element time delay fuse should be calculated at 175% (1.75) of the full-load current rating for an alternating current (AC) polyphase (three-phase) squirrel cage inductor motor.
In this scenario, the squirrel cage inductor motor didn't list a NEMA design code on its nameplate. Thus, we'll assume that the inductor motor is design B and its fuse rating is given by:
Fuse rating = 248 × 1.75 × 434
In conclusion, the nearest standard fuse size which is above the computed value listed in Section 240.6 of the National Electrical Code (NEC) is 450 amperes.
Read more on National Electrical Code here: brainly.com/question/10619436