Gauge pressure is a relative measurement based on atmospheric pressure. Gauge pressure can be positive if it is above atmospheric pressure or it can also be negative it is below. On another hand, absolute pressure is an actual pressure in a space and its value has always to be zero or above. Basically absolute pressure is zero if it is in a perfect vacuum. So the measurement of absolute pressure is gauge pressure + atmospheric pressure. This is the reason in normal condition the gauge pressure = absolute pressure - atmospheric pressure and therefore is lower than absolute pressure
Answer:
Explanation:
Before: PT= 0.10, PB= 0.03 (given) ET = 2.5 ER = 2.0 (Table 6.5)
fHV= 0.847 (Eq. 6.5) PHF = 0.95, fp= 0.90, N=2, V = 2200 (given)
vp= V/[PHF⋅fHVTB⋅fp⋅N] = 1518.9 (Eq. 6.3)
BFFS = 50+5, BFFS =55 (given) fLW= 6.6
TLC=6+3=9 fLC= 0.65
fM= 0.0
fA= 1.0
FFS = BFFS −fLW−fLC–fM–fA= 46.75 (Eq. 6.7)
Use FFS=45 D= vp/S = 33.75pc/mi/ln Eq (6.6)
After: fA= 3.0
FFS = BFFS −fLW−fLC–fM–fA= 44.75 (Eq. 6.7)
Use FFS=45 Vnew= 2600 Vp= Va/[PHF⋅fHB⋅fp⋅N] = 1795 (Eq. 6.3) D= vp/S = 39.89pc/mi/ln
Given:
voltage, V = 3600V
step-up voltage, V' = 100000 V
Resistance of line, 
Solution:
To calculate % heat loss in long distance power line:
Power produced by AC generator, P =
W
P = 180000 W = 180 kW
At step-up voltage, V = 100000V or 100 kV
current, I = 
I = 
I = 1.8 A
Power line voltage drop is given by:



Power dissipated in long transmission line 
Power dissipated in long transmission line
= 324 W
% Heat loss in power line, 
% Heat loss in power line, 