Answer:
(a). The reactive power is 799.99 KVAR.
(c). The reactive power of a capacitor to be connected across the load to raise the power factor to 0.95 is 790.05 KVAR.
Explanation:
Given that,
Power factor = 0.6
Power = 600 kVA
(a). We need to calculate the reactive power
Using formula of reactive power
...(I)
We need to calculate the 
Using formula of 

Put the value into the formula


Put the value of Φ in equation (I)


(b). We draw the power triangle
(c). We need to calculate the reactive power of a capacitor to be connected across the load to raise the power factor to 0.95
Using formula of reactive power


We need to calculate the difference between Q and Q'

Put the value into the formula


Hence, (a). The reactive power is 799.99 KVAR.
(c). The reactive power of a capacitor to be connected across the load to raise the power factor to 0.95 is 790.05 KVAR.
Explanation:
hope this answer was helpful
ohm's law V=IR
V=24x11=240+24=264V
About mains and dangerous needs insulating
The base unit of length in the international system of units is the: meter (m)
<h3>Meter</h3>
The meter, ( symbol: m ) is the SI unit of length. It is derived by taking the fixed numerical value of the speed of light in vacuum c to be 299 792 458 when expressed in the unit m s-1
<h3>International system of unit ( SI ) base units</h3>
The SI base units are the standard units of measurement defined which is defined by the International System of Units (SI) for the seven base quantities of what is now known as the International System of quantities:
Learn more about SI base units:
brainly.com/question/16393390