Answer: 45 A
Explanation:
Primary only protection 3-phase
I = 3 phase kVA / ( 1.723 * V)
I = 30000 / ( 1.732 * 480 ) = 36.085 A
Table 450.3(B)
Currents of 9A or more column
primary only protection = 125%
Max OCPD pri = 125% of I = 1.25 * 36.085 = 45.11 A
Table 450.3(B) Note 1 does not apply, use next smaller Table 240.6(A)
Next smaller = 45 A