Answer:
hello some parts of your question is missing attached below is the missing part ( the required fig and table )
answer : The solar collector surface area = 7133 m^2
Explanation:
Given data :
Rate of energy input to the collectors from solar radiation = 0.3 kW/m^2
percentage of solar power absorbed by refrigerant = 60%
Determine the solar collector surface area
The solar collector surface area = 7133 m^2
attached below is a detailed solution of the problem
Answer:
Relative humidity 48%.
Dew point 74°F
humidity ratio 118 g of moisture/pound of dry air
enthalpy 41,8 BTU per pound of dry air
Explanation:
You can get this information from a Psychrometric chart for water, like the one attached.
You enter the chart with dry-bulb and wet-bulb temperatures (red point in the attachment) and following the relative humidity curves you get approximately 48%.
To get the dew point you need to follow the horizontal lines to the left scale (marked with blue): 74°F
for the humidity ratio you need to follow the horizontal lines but to the rigth scale (marked with green): 118 g of moisture/pound of dry air
For enthalpy follow the diagonal lines to the far left scale (marked with yellow): 41,8 BTU per pound of dry air
Answer:
i don't think i understand the question
Explanation: