A block of ice weighing 20 lb is taken from the freezer where it was stored at -15"F. How many Btu of heat will be required to c

onvert the ice to water at 200°F?
Engineering
1 answer:
Rus_ich [418]3 years ago
8 0

Answer:

Heat required =7126.58 Btu.

Explanation:

Given that

Mass m=20 lb

We know that

1 lb =0.45 kg

So 20 lb=9 kg

m=9 kg

Ice at -15° F and we have to covert it at 200° F.

First ice will take sensible heat at up to 32 F then it will take latent heat at constant temperature and temperature will remain 32 F.After that it will convert in water and water will take sensible heat and reach at 200 F.

We know that

Specific heat for ice C_p=2.03\ KJ/kg.K

Latent heat for ice H=336 KJ/kg

Specific heat for ice C_p=4.187\ KJ/kg.K

We know that sensible heat given as

Q=mC_p\Delta T

Heat for -15F to 32 F:

Q=mC_p\Delta T

Q=9\times 2.03(32+15) KJ

Q=858.69 KJ

Heat for 32 Fto 200 F:

Q=mC_p\Delta T

Q=9\times 4.187(200-32) KJ

Q=6330.74 KJ

Total heat=858.69 + 336 +6330.74 KJ

Total heat=7525.43 KJ

We know that 1 KJ=0.947 Btu

So   7525.43 KJ=7126.58 Btu

So heat required to covert ice into water is 7126.58 Btu.

You might be interested in
Explain 3 ways that people in sports use engineering to increase their performance?
LenKa [72]
Designing systems for manufacturing, motion analysis or impact testing;
building and testing prototypes;
analyzing the human body to prevent injury;
developing or designing new light weight materials that will be more comfortable and withstand greater impacts or forces;
7 0
3 years ago
It is possible to maintain a pressure of 10 kPa in a condenser that is being cooled by river water entering at 20 °C?
vovangra [49]

Answer:

Yes, it is possible to maintain a pressure of 10 kPa in a condenser that is being cooled by river water that is entering at 20 °C because this temperature (20 °C) of the external cooling water is less than the saturation temperature of steam which is which is 45.81 °C, and heated by a boiler; as a result of this condition, coupled with the assumption that the turbine, pump, and interconnecting tube are adiabatic, and the condenser exchanges its heat with the external cooling river water, it possible to maintain a pressure of 10 kPa.

5 0
3 years ago
A home electrical system is joined to the electric company's system at the junction of the
aleksandrvk [35]

That would be B, I hope this helps!

5 0
2 years ago
A cylinder fitted with a frictionless piston contains 2 kg of R-134a at 3.5 bar and 100 C. The cylinder is now cooled so that th
inna [77]

Answer:

The answer to the question is

The heat transferred in the process is -274.645 kJ

Explanation:

To solve the question, we list out the variables thus

R-134a = Tetrafluoroethane

Intitial Temperaturte t₁ = 100 °C

Initial pressure = 3.5 bar = 350 kPa

For closed system we have m₁ = m₂ = m

ΔU = m×(u₂ - u₁) = ₁Q₂ -₁W₂

For constant pressure process we have

Work done = W = \int\limits^a_b P \, dV  = P×ΔV = P × (V₂ - V₁) = P×m×(v₂ - v₁)

From the tables we have

State 1 we have h₁ = (490.48 +489.52)/2 = 490 kJ/kg

State 2 gives h₂ = 206.75 + 0.75 × 194.57= 352.6775 kJ/kg

Therefore Q₁₂ = m×(u₂ - u₁) + W₁₂ = m × (u₂ - u₁) + P×m×(v₂ - v₁)

= m×(h₂ - h₁) = 2.0 kg × (352.6775 kJ/kg - 490 kJ/kg) =-274.645 kJ

5 0
3 years ago
A device that transforms electrical energy to mechanical:
xxTIMURxx [149]

Answer:

electric motor

*** brainly if possible

Explanation:

3 0
2 years ago
Other questions:
  • A 300 mm long steel bar with a square cross section (25 mm per edge) is pulled in tension with a load of 83,051 N , and experien
    10·1 answer
  • An air compressor of mass 120 kg is mounted on an elastic foundation. It has been observed that, when a harmonic force of amplit
    13·1 answer
  • Air is to be heated steadily by an 8-kW electric resistance heater as it flows through an insulated duct. If the air enters at 5
    10·1 answer
  • What causes decay in the amplitudes of vibration?
    11·1 answer
  • Let CFG G be the following grammar.
    7·2 answers
  • Two engineers are to solve an actual heat transfer problem in a manufacturing facility. Engineer A makes the necessary simplifyi
    14·1 answer
  • It's in the picture please asap
    6·2 answers
  • Factors such as brake shoe orientation, pin location, and direction of rotation determine whether a particular brake shoe is con
    12·1 answer
  • Which symbol should be used for the given scenario?
    11·1 answer
  • thanh thẳng AD có kích thước và chịu lực như hình.biết P1 = 10kn, p2=5kn,M=15kn*m,a=2m.Hãy xách định phản lực liên kết tại A,b
    14·1 answer
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!