Citrus2011 [14]
3 years ago
10

What is the difference between pound-mass and pound-force?

Engineering
1 answer:
vichka [17]3 years ago
8 0

Answer:

Pound mass is the unit of mass and which is used in United states customary to describe the mass Slug is also a unit of mass .Pound mass is lbm. But on the other hand pound force is the unit of force.Pound force is lbf.

In SI unit ,the unit of mass is kilogram(kg) and the unit of force is Newton(N)

In CGS system the unit of mass is gram and unit of force is dyne.

You might be interested in
Even when you have the right-of-way, you're responsible for _____ before you drive forward.
Mazyrski [523]

Answer: look left to right twice b/c somebody may try to run the light

Explanation:

3 0
3 years ago
Read 2 more answers
A piston-cylinder device contains 0.1 m3 of liquid water and 0.9 m² of water vapor in equilibrium at 800 kPa. Heat is transferre
docker41 [41]

Answer:

Initial temperature = 170. 414 °C

Total mass = 94.478 Kg

Final volumen = 33.1181 m^3

Diagram  = see picture.

Explanation:

We can consider this system as a close system, because there is not information about any output or input of water, so the mass in the system is constant.  

The information tells us that the system is in equilibrium with two phases: liquid and steam. When a system is a two phases region (equilibrium) the temperature and pressure keep constant until the change is completed (either condensation or evaporation). Since we know that we are in a two-phase region and we know the pressure of the system, we can check the thermodynamics tables to know the temperature, because there is a unique temperature in which with this pressure (800 kPa) the system can be in two-phases region (reach the equilibrium condition).  

For water in equilibrium at 800 kPa the temperature of saturation is 170.414 °C which is the initial temperature of the system.  

to calculate the total mass of the system, we need to estimate the mass of steam and liquid water and add them. To get these values we use the specific volume for both, liquid and steam for the initial condition. We can get them from the thermodynamics tables.

For the condition of 800 kPa and 170.414 °C using the thermodynamics tables we get:

Vg (Specific Volume of Saturated Steam) = 0.240328 m^3/kg

Vf (Specific Volume of Saturated Liquid) = 0.00111479 m^3/kg

if you divide the volume of liquid and steam provided in the statement by the specific volume of saturated liquid and steam, we can obtain the value of mass of vapor and liquid in the system.

Steam mass = *0.9 m^3 / 0.240328 m^3/kg = 3.74488 Kg

Liquid mass = 0.1 m^3 /0.00111479 m^3/kg = 89.70299 Kg  

Total mass of the system = 3.74488 Kg + 89.70299 Kg = 93,4478 Kg

If we keep the pressure constant increasing the temperature the system will experience a phase-change (see the diagram) going from two-phase region to superheated steam. When we check for properties for the condition of P= 800 kPa and T= 350°C we see that is in the region of superheated steam, so we don’t have liquid water in this condition.  

If we want to get the final volume of the water (steam) in the system, we need to get the specific volume for this condition from the thermodynamics tables.  

Specific Volume of Superheated Steam at 800 kPa and 350°C = 0.354411 m^3/kg

We already know that this a close system so the mass in it keeps constant during the process.

 

If we multiply the mass of the system by the specific volume in the final condition, we can get the final volume for the system.  

Final volume = 93.4478 Kg * 0.354411 m^3/kg = 33.1189 m^3

You can the P-v diagram for this system in the picture.  

For the initial condition you can calculate the quality of the steam (measure of the proportion of steam on the mixture) to see how far the point is from for the condition on all the mix is steam. Is a value between 0 and 1, where 0 is saturated liquid and 1 is saturated steam.  

Quality of steam = mass of steam / total mass of the system

Quality of steam = 3.74488 Kg /93.4478 Kg = 0,040 this value is usually present as a percentage so is 4%.  

Since this a low value we can say that we are very close the saturated liquid point in the diagram.  

6 0
4 years ago
An air conditioner operating at steady state maintains a dwelling at 70°F on a day when the outside temperature is 99°F. The rat
IrinaVladis [17]

Answer:

a) the coefficient of performance of the air conditioner is 3.5729

b)

- the power input required for a reversible air conditioner is 0.645 hp

- the coefficient of performance for the reversible air conditioner is 18.2759

Explanation:

Given the data in the question;

Lower Temperature T_L = 70°F = ( 70 + 460 )R = 530 R

Higher Temperature T_H = 99° F = ( 99 + 460 )R = 559 R

Cooling Load Q_L = 30000 Btu/h

we know that 1 hp = 2544.43 Btu/h

Net power input P = 3.3 hp = ( 3.3 × 2544.43 )Btu/h = 8396.619 Btu/h

a)

Coefficient of performance of the air conditioner;

COP_{air-condition = Cooling Load Q_L  / power P

we substitute

COP_{air-condition = 30000 Btu/h / 8396.619 Btu/h

COP_{air-condition = 3.5729

Therefore, the coefficient of performance of the air conditioner is 3.5729

b)

- Power input required ( in hp )

Q_L / P_{required = T_L / ( T_H - T_L )

we substitute

30000 Btu/h / P_{required = 530 R / ( 559 R - 530 R )

30000 Btu/h / P_{required = 530 R / 29 R

we solve for P_{required

P_{required  = ( 30000 Btu/h × 29 R ) / 530 R

P_{required  = ( 870000 Btu/h / 530 )

P_{required  = 1641.5094 Btu/h

we know that; 1 hp = 2544.43 Btu/h

so;

P_{required  = ( 1641.5094 / 2544.43 ) hp

P_{required  = 0.645 hp

Hence, the power input required for a reversible air conditioner is 0.645 hp

- the coefficient of performance for the reversible air conditioner;

COP_{rev-air-condition = T_L / ( T_H - T_L )

we substitute

COP_{rev-air-condition = 530 R / ( 559 R - 530 R )

COP_{rev-air-condition = 530 R / 29 R

COP_{rev-air-condition = 18.2759

Hence, the coefficient of performance for the reversible air conditioner is 18.2759

3 0
3 years ago
In vehicles equipped with an anti-braking system the drivers foot must remain firmly on the
Murrr4er [49]
... brake pedal; In vehicles equipped with ABS, the driver's foot remains firmly on the brake pedal, allowing the system to automatically pump the brakes.

“Brake Pedal.”
3 0
3 years ago
Read 2 more answers
Explain how use of EGR is effective in reducing NOx emissions 4. In most locations throughout the U.S., the octane number of reg
TiliK225 [7]

Answer:please see attached file

Explanation:

3 0
4 years ago
Other questions:
  • Why do we study economics
    13·1 answer
  • The uniform beam is supported by two rods AB and CD that have crosssectional areas of 10 mm2 and 15 mm2 , respectively. Determin
    5·1 answer
  • 1. When two vehicles moving at the same speed are involved in a collision, the vehicle that
    15·1 answer
  • How can we prevent chemical hazards in labotary
    9·1 answer
  • In order to reduce the waiting time further, a traffic light was installed to replace the yield sign. Assuming the departure pro
    5·1 answer
  • Explain 4 things you can do with a Combination Square
    5·1 answer
  • "Compute the flow time, tardiness, and lateness for each job, and the average flow time, average tardiness, and average lateness
    10·1 answer
  • Coderz robotics 101: challenge mission 3 part 3
    8·1 answer
  • What is an OTG USB? how is it useful ​
    14·1 answer
  • Consider a 25-mm-diameter and 15-m-long smooth tube that is maintained at a constant surface temperature. Fluids enter the tube
    12·1 answer
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!