Answer:
(a) The proportion of dry air bypassing the unit is 14.3%.
(b) The mass of water removed is 1.2 kg per 100 kg of dry air.
Explanation:
We can express the proportion of air that goes trough the air conditioning unit as
and the proportion of air that is by-passed as
, being
.
The amount of water that goes into the drier inlet has to be 0.004 kg/kg, and can be expressed as:
![0.004 = 0.016*p_{bp}+ 0.002*p_{d}](https://tex.z-dn.net/?f=0.004%20%3D%200.016%2Ap_%7Bbp%7D%2B%200.002%2Ap_%7Bd%7D)
Replacing the first equation in the second one we have
![0.004 = 0.016*(1-p_{d})+ 0.002*p_{d}=0.016-0.016*p_{d}+0.002*p_{d}\\0.004 - 0.016 = (-0.016+0.002)*p_{d}\\-0.012 = -0.014*p_{d}\\p_{d}=\frac{-0.012}{-0.014}=0.857\\\\p_{bp}=1-p_{d}=1-0.857=0.143](https://tex.z-dn.net/?f=0.004%20%3D%200.016%2A%281-p_%7Bd%7D%29%2B%200.002%2Ap_%7Bd%7D%3D0.016-0.016%2Ap_%7Bd%7D%2B0.002%2Ap_%7Bd%7D%5C%5C0.004%20-%200.016%20%3D%20%28-0.016%2B0.002%29%2Ap_%7Bd%7D%5C%5C-0.012%20%3D%20-0.014%2Ap_%7Bd%7D%5C%5Cp_%7Bd%7D%3D%5Cfrac%7B-0.012%7D%7B-0.014%7D%3D0.857%5C%5C%5C%5Cp_%7Bbp%7D%3D1-p_%7Bd%7D%3D1-0.857%3D0.143)
(b) Of every kg of dry air feed, 85.7% goes in to the air conditioning unit.
It takes (0.016-0.002)=0.014 kg water per kg dry air feeded.
The water removed of every 100 kg of dry air is
![100 kgDA*0.857*0.014 kgW/kgDA= 1.1998 \approx 1.2 kgW](https://tex.z-dn.net/?f=100%20kgDA%2A0.857%2A0.014%20kgW%2FkgDA%3D%201.1998%20%5Capprox%201.2%20kgW)
It can also be calculated as the difference in humiditiy between the inlet and the outlet: (0.016-0.004=0.012 kgW/kDA) and multypling by the total amount of feed (100 kgDA).
100 * 0.012 = 1.2 kgW