Dear Student, this question is incomplete, and to attempt this question, we have attached the complete copy of the question in the image below. Please, Kindly refer to it when going through the solution to the question.
To objective is to find the:
(i) required heat exchanger area.
(ii) flow rate to be maintained in the evaporator.
Given that:
water temperature = 300 K
At a reasonable depth, the water is cold and its temperature = 280 K
The power output W = 2 MW
Efficiency
= 3%
where;



However, from the evaporator, the heat transfer Q can be determined by using the formula:
Q = UA(L MTD)
where;

Also;




LMTD = 4.97
Thus, the required heat exchanger area A is calculated by using the formula:

where;
U = overall heat coefficient given as 1200 W/m².K

The mass flow rate:

External = R
Internal = r
Volume of hemisperical = 2/3 π(R³-r³)
V= 2/3 π(9.1³ - 8.4³)
V= 336.9 cm³
Answer:
Explained
Explanation:
Along some shorelines, incoming waves cause the water to simply rise and fall and not form surfs because of the steepness of the shorelines. Long period waves wont form surfs at steep shores because of the breaking and unstability of waves. Wave breaks at the shallow waters. The breaking of the waves depends upon H/L ratio.
Answer:
Resistance to electrical currents
Explanation:
Conductors have low resistance to electrical currents, and are used to "conduct" the flow of electricity.
Insulators have very high resistance and are used to protect us from the flow of electricity.
Acetic acid is a weak acid and sodium hydroxide is strong base. Salts of the two will hydrolyse to give basic solution. So, at neutral point, pH of the solution will be greater than 8.