In this case, we compute the heat output from coal, given its heating value and the mass flow:

Next, since the work done by the power plant is 230 MW, we compute the efficiency as shown below:

Best regards!
Answer:
The three phase full load secondary amperage is 2775.7 A
Explanation:
Following data is given,
S = Apparent Power = 1000 kVA
No. of phases = 3
Secondary Voltage: 208 V/120 V <em>(Here 208 V is three phase voltage and 120 V is single phase voltage) </em>
<em>Since,</em>
<em />
<em />
<em />

The formula for apparent power in three phase system is given as:

Where:
S = Apparent Power
V = Line Voltage
I = Line Current
In order to calculate the Current on Secondary Side, substituting values in above formula,

Answer:
increases by a factor of 6.
Explanation:
Let us assume that the initial cross sectional area of the pipe is A m² while the initial velocity of the water is V m/s², hence the flow rate of the water is:
Initial flow rate = area * velocity = A * V = AV m³/s
The water speed doubles (2V m/s) and the cross-sectional area of the pipe triples (3A m²), hence the volume flow rate becomes:
Final flow rate = 2V * 3A = 6AV m³/s = 6 * initial flow rate
Hence, the volume flow rate of the water passing through it increases by a factor of 6.