Answer:
Relative humidity 48%.
Dew point 74°F
humidity ratio 118 g of moisture/pound of dry air
enthalpy 41,8 BTU per pound of dry air
Explanation:
You can get this information from a Psychrometric chart for water, like the one attached.
You enter the chart with dry-bulb and wet-bulb temperatures (red point in the attachment) and following the relative humidity curves you get approximately 48%.
To get the dew point you need to follow the horizontal lines to the left scale (marked with blue): 74°F
for the humidity ratio you need to follow the horizontal lines but to the rigth scale (marked with green): 118 g of moisture/pound of dry air
For enthalpy follow the diagonal lines to the far left scale (marked with yellow): 41,8 BTU per pound of dry air
Answer:
The electrical power is 96.5 W/m^2
Explanation:
The energy balance is:
Ein-Eout=0

if:
Gsky=oTsky^4
Eb=oTs^4
qc=h(Ts-Tα)


if Gl≈El(l,5800)

lt= 2*5800=11600 um-K, at this value, F=0.941

The hemispherical emissivity is equal to:

lt=2*333=666 K, at this value, F=0

The hemispherical absorptivity is equal to:

Answer:
All 3 principal stress
1. 56.301mpa
2. 28.07mpa
3. 0mpa
Maximum shear stress = 14.116mpa
Explanation:
di = 75 = 0.075
wall thickness = 0.1 = 0.0001
internal pressure pi = 150 kpa = 150 x 10³
torque t = 100 Nm
finding all values
∂1 = 150x10³x0.075/2x0,0001
= 0.5625 = 56.25mpa
∂2 = 150x10³x75/4x0.1
= 28.12mpa
T = 16x100/(πx75x10³)²
∂1,2 = 1/2[(56.25+28.12) ± √(56.25-28.12)² + 4(1.207)²]
= 1/2[84.37±√791.2969+5.827396]
= 1/2[84.37±28.33]
∂1 = 1/2[84.37+28.33]
= 56.301mpa
∂2 = 1/2[84.37-28.33]
= 28.07mpa
This is a 2 d diagram donut is analyzed in 2 direction.
So ∂3 = 0mpa
∂max = 56.301-28.07/2
= 14.116mpa
I don’t see the the picture?