Given:
Network rated voltage = 24 kV
Impedance of network = 0.07 + j0.5 Ω/mi, 8 mi
Rn = 0.07 * 8 = 0.56 Ω
Xn = 0.5 * 8 = 4 Ω
If the alternator terminal voltage is equal to network rated voltage will have
Vt = 24 kV/√3 = 13.85 kV/phase
The alternative current is
The impedance Zn is
The voltage drop is
rac = 1.2rdc = 1.2 * 7.476 = 8.97 Ω
The effective armature resistance is
The induced voltage for leading power factor is
if cosθ = 0.5
if cosθ= 0.6
EF = 12790.8 V
if cosθ = 0.7
EF = 13731.05 V
if cosθ = 0.8
EF = 14741.6 V
if cosθ = 0.9
EF = 15809.02 V
if cosθ = 1
EF = 13975.6 V
The voltage regulation is
For each value:
if cosθ = 0.5
voltage regulation = -13.8%
if cosθ = 0.6
voltage regulation = -7.6%
if cosθ = 0.7
voltage regulation = -0.85%
if cosθ = 0.8
voltage regulation = 6.4%
if cosθ = 0.9
voltage regulation = 14%
if cosθ = 1
voltage regulation = 0.9%
the graph is shown in the attached image
for 10% of regulation the power factor is 0.81