Answer:
The three phase full load secondary amperage is 2775.7 A
Explanation:
Following data is given,
S = Apparent Power = 1000 kVA
No. of phases = 3
Secondary Voltage: 208 V/120 V <em>(Here 208 V is three phase voltage and 120 V is single phase voltage) </em>
<em>Since,</em>
<em />
<em />
<em />

The formula for apparent power in three phase system is given as:

Where:
S = Apparent Power
V = Line Voltage
I = Line Current
In order to calculate the Current on Secondary Side, substituting values in above formula,

Answer:
Answer: ±0.02 units or 20±0.02 units or 19.98-20.02 units depending on how they prefer its written (typically the first or second one)
Explanation:
says on the sheet. Unless otherwise stated 0.XX = ±0.02 tolerance
(based on image sent in other post)
Answer:
The answer is A.
Explanation:
Two main types of network switches, modular and fixed configuration switches, are used for connecting the devices with one another provided they are on the same network.
As the name suggests, modular switches can be configured according to your needs and specific situations where you need a different setup.
The one advantage fixed-configuration switches have over the modular switches is that they are easier to operate. You can't change anything for a different application but they are simpler to setup and use, you can just plug them in and start using. They are usually for the more casual end-user and home networks etc.
I hope this answer helps.
Answer:
B) An increase in pressure can lower the boiling point of a liquid and change the temperature at which it turns to a gas.
Explanation:
B) An increase in pressure can lower the boiling point of a liquid and change the temperature at which it turns to a gas.