Answer:
41.053 A
Explanation:
given,
three phase kVA = 25-kVA
voltage = 440 Volt
current = ?
To determine three phase kVA when volts and amperes are know
three phase kVA = 1.73 x V x I


I = 32.84 A
the maximum overcurrent protection value is equal to
= 125 % of I
= 1.25 x 32.84
= 41.053 A