Explanation:
This means that for every 1 cm on the drawing, there is 80 cm in reality. To put it another way, take this
1:80 means that the building is 80 times the size of the drawing
80:1 means that the drawing is 80 times the size of the building
If it were 80:1, the drawing itself would be over 100m long.
Answer:
COP of heat pump=3.013
COP of cycle=1.124
Explanation
W = Q2 - Q1 ----- equation 1
W = work done
Q2 = final energy
Q1 = initial energy
A) calculate the COP of the heat pump
COP =Q2/W
from equation 1
Q2 = Q1 + W = 15 + 7.45 = 22.45 KW
therefore COP =22.45/7.45 = 3.013
B) COP when cycle is reversed
COP = Q1/W
from equation 1
Q1 + W = Q2 ------ equation 2
Q2 = 15 Btu/s = 15 * 1.055 = 15.825 KW therefore from equation 2
Q1 = 8.375 KW
COP =8.375/7.45 = 1.124
Answer:
810 g
Explanation:
Mass is the product of density and volume:
m = ρV
m = (8.1 g/cm³)(100 cm³) = 810 g
The mass of the chunk is 810 grams.
Answer:
Given that the temperature of the window is below the dew point it will condensate.
Explanation:
A psychrometric chart (like the one attached) will give you the information needed. This chart is for 14.696 psia.
On the bottom horizontal axes you have the dry-bulb temperature, in this case 70°F, going up from this point you can reach the 50% relative humidity curve (red point on chart), going horizontally from this point to the 100% relative humidity you get the dew point temperature (the point at which moisture will condensate) (blue point on chart). In this case the dew point is 50°C. Given that the temperature of the window is below the dew point it will condensate.