Answer:
≈ 18.62 kw
Explanation:
Given data :
Diversity factor among transformer = 1.3
No of transformers load demand factor diversity factor
Transformer 1 10 kw 0.65 1.5
Transformer 2 12 kw 0.6 3.5
Transformer 3 15 kw 0.7 1.5
calculate the maximum load on the feeder
demand factor = max demand / load
Max demand = demand factor * load
max demands:
Transformer 1 = 0.65 * 10 = 6.5
Transformer 2 = 0.6 * 12 = 7.2
Transformer 3 = 0.7 * 15 = 10.5
Diversity factor = ( summation of max demands ) / maximum load on feeder
1.3 = ( 6.5 +7.2 + 10.5 ) / max load on feeder
hence : max load on feeder = 24.2 / 1.3 = 18.62 kw