Answer:
the maximum thermal efficiency is 29%
Explanation:
the maximum efficiency for a thermal engine that works between a cold source and a hot source is the one of a Carnot engine. Its efficiency is given by
Maximum efficiency= 1 - T2/T1
where
T2= absolute temperature of the cold sink (environment)= 20°C + 273 = 293
T2= absolute temperature of the hot source (hot water supply) = 140°C + 273 = 413
therefore
Maximum efficiency= 1 - T2/T1 = 1 - 293/413 = 0,29 =29%
Answer:
a) 
Explanation:
a) Let consider that heat pump is reversible, so that the Coefficient of Performance is:



The minimum heat received by the house must be equal to the heat lost to keep the average temperature constant. Hence:

The minimum power supplied to the heat pump is:



The answer for this question is A