sdas [7]
3 years ago
9

A three-phase line has an impedance of 0.4 j2.7 ohms per phase. The line feeds two balanced three-phase loads that are connected

in parallel. The first load is absorbing 560.1kVA at 0.707 power factor lagging. The second load absorbs 132 kW at unity power factor. The line-to-line voltage at the load end of the line is 3810.5 volts. Determine: a. The magnitude of the line voltage at the source end of the line. b. Total real and reactive power loss in the line. c. Real power and reactive power supplied at the sending end of the line.
Engineering
1 answer:
Viktor [21]3 years ago
7 0

Answer:

a. The magnitude of the line source voltage is

Vs = 4160 V

b. Total real and reactive power loss in the line is

Ploss = 12 kW

Qloss = j81 kvar

Sloss = 12 + j81 kVA

c. Real power and reactive power supplied at the sending end of the line

Ss = 540.046 + j476.95 kVA

Ps = 540.046 kW

Qs = j476.95 kvar

Explanation:

a. The magnitude of the line voltage at the source end of the line.

The voltage at the source end of the line is given by

Vs = Vload + (Total current×Zline)

Complex power of first load:

S₁ = 560.1 < cos⁻¹(0.707)

S₁ = 560.1 < 45° kVA

Complex power of second load:

S₂ = P₂×1 (unity power factor)

S₂ = 132×1

S₂ = 132 kVA

S₂ = 132 < cos⁻¹(1)

S₂ = 132 < 0° kVA

Total Complex power of load is

S = S₁ + S₂

S = 560.1 < 45° + 132 < 0°

S = 660 < 36.87° kVA

Total current is

I = S*/(3×Vload)   ( * represents conjugate)

The phase voltage of load is

Vload = 3810.5/√3

Vload = 2200 V

I = 660 < -36.87°/(3×2200)

I = 100 < -36.87° A

The phase source voltage is

Vs = Vload + (Total current×Zline)

Vs = 2200 + (100 < -36.87°)×(0.4 + j2.7)

Vs = 2401.7 < 4.58° V

The magnitude of the line source voltage is

Vs = 2401.7×√3

Vs = 4160 V

b. Total real and reactive power loss in the line.

The 3-phase real power loss is given by

Ploss = 3×R×I²

Where R is the resistance of the line.

Ploss = 3×0.4×100²

Ploss = 12000 W

Ploss = 12 kW

The 3-phase reactive power loss is given by

Qloss = 3×X×I²

Where X is the reactance of the line.

Qloss = 3×j2.7×100²

Qloss = j81000 var

Qloss = j81 kvar

Sloss = Ploss + Qloss

Sloss = 12 + j81 kVA

c. Real power and reactive power supplied at the sending end of the line

The complex power at sending end of the line is

Ss = 3×Vs×I*

Ss = 3×(2401.7 < 4.58)×(100 < 36.87°)

Ss = 540.046 + j476.95 kVA

So the sending end real power is

Ps = 540.046 kW

So the sending end reactive power is

Qs = j476.95 kvar

You might be interested in
The best way to identify common masonry problems is to call the engineer.<br> True or False
Daniel [21]

Answer:

True

Explanation:

5 0
2 years ago
Briefly discuss if it would be better to operate with pumps in parallel or series and how your answer would change as the steepn
Aleksandr [31]

Answer:

1) In series, the combined head will move from point 1 to point 2 in theory. However, practically speaking, the combined head and flow rate will move along the system curve to point 3.

2) In parallel, the combined head and volume flow will move along the system curve from point 1 to point 3.

Explanation:

1) Pump in series:

When two or more pumps are connected in series, their resulting pump performance curve will be obtained by adding their respective heads at the same flow rate as shown in the first diagram attached.

In the first diagram, we have 3 curves namely:

- system curve

- single pump curve

- 2 pump in series curve

Also, we have points labeled 1, 2 and 3.

- Point 1 represents the point that the system operates with one pump running.

- Point 2 represents the point where the head of two identical pumps connected in series is twice the head of a single pump flowing at the same rate.

- Point 3 is the point where the system is operating when both pumps are running.

Now, since the flowrate is constant, the combined head will move from point 1 to point 2 in theory. However, practically speaking, the combined head and flow rate will move along the system curve to point 3.

2) Pump in parallel:

When two or more pumps are connected in parallel, their resulting pump performance curve will be obtained by adding their respective flow rates at same head as shown in the second diagram attached.

In the second diagram, we have 3 curves namely:

- system curve

- single pump curve

- 2 pump in series curve

Also, we have points labeled 1, 2 and 3

- Point 1 represents the point that the system operates with one pump running.

- Point 2 represents the point where the flow rate of two identical pumps connected in series is twice the flow rate of a single pump.

- Point 3 is the point where the system is operating when both pumps are running.

In this case, the combined head and volume flow will move along the system curve from point 1 to point 3.

5 0
2 years ago
Because assembly language is so close in nature to machine language, it is referred to as a ____________.
My name is Ann [436]

Answer:

symbolic machine code.

Explanation:

The instructions in the language are closely linked to the machine's architecture.

5 0
3 years ago
Identify and describe the three stages of a life cycle analysis.
sesenic [268]
The LCA process is a systematic, phased approach and consists of four components: goal definition and scoping, inventory analysis, impact assessment, and interpretation. The standards are provided by the International Organisation for Standardisation (ISO) in ISO 14040 and 14044, and describe the four main phases of an LCA: Goal and scope definition. Inventory analysis. Impact assessment.

Hope this is helpful
5 0
2 years ago
Identify one of the advantages of 3d modeling?
Naddik [55]

Answer:

Hello Adam here! (UWU)

Explanation:

The advantages of 3D modeling for designers is not limited to productivity and coordination, it is an excellent communication tool for both the designer and end user. 3D models can help spark important conversations during the design phase and potentially avoid costly construction mishaps.

Happy to Help! (>.O)

6 0
3 years ago
Other questions:
  • A food department is kept at -12 °C by a refrigerator in an environment at 30 °C. The total heat gain to the food department is
    8·1 answer
  • 6.Identification of Material ParametersThe principal in-plane stresses and associated strains in a plate of material areσ1= 50 k
    5·1 answer
  • A mass of 8000 kg of slightly enriched uranium (2% U-235, 98% U-238) is exposed for 30 days in a reactor operating at (6.18) hea
    5·1 answer
  • A 100 kmol/h stream that is 97 mole% carbon tetrachloride (CCL) and 3% carbon disulfide (CS2) is to be recovered from the bottom
    7·1 answer
  • Create a function (prob3_5) that will take inputs of vectors x and y in feet, scalar N, scalars L and W in feet and scalars T1 a
    6·1 answer
  • Fix the code so the program will run correctly for MAXCHEESE values of 0 to 20 (inclusive). Note that the value of MAXCHEESE is
    8·1 answer
  • How does java achieve portable
    13·1 answer
  • which systems engineering support discipline has the goal to ensure that support considerations are an integral part of the syst
    14·1 answer
  • How many astronauts work<br> in the International Space Station
    7·1 answer
  • The volume of microbial culture is observed to increase according to the formula
    15·1 answer