The technician should start by checking the temperature rise across the indoor coil.
<h3>Who is a technician?</h3>
This is a person who has skill in a particular area of job. A technician is responsible for repairs and also ensure different equipment and systems are working perfectly.
Hence, the technician should start by checking the temperature rise across the indoor coil.
Learn more about technician here : brainly.com/question/13315405
#SPJ1
Answer:
Check the explanation
Explanation:
Question 1.
The secondary current of 250/5 amps CT when 300 amps(rated current of transmission line ) flow in TL is
(5/250 ) X 300 = 6 amps
Question 2
The correct answer to this second question is yes, when Over current relay coil will operate and relay contacts gets close, if the pickup value( Ip) of relay is set as 6 amps in relay. ( because primary current of TL is 1.2 times of CT primary)
Question 3
Tap Block figure (Fig 1) is not available/uploaded in your question.
Answer:
YES
Explanation:
If we connect batteries in series then the output voltage is the sum of the individual voltage of each battery i.e if you connect three 12 volts batteries in series then their output voltage will be 12+12+12=36 volts, but the current rating of the batteries in series will be same of the individual battery rating in 'mah'.
But when we connect the batteries in parallel their voltage is not added but their current rating in mah is addition of their individual rating.
So, If you want 24 volts from three 12 volts battery then you can connect two of them in series and the other one in parallel with them this will give 24 volts and the current will be addition of the two series batteries and the third which is in parallel with them. You can use this configuration if current value is not a big factor.