Tema [17]
3 years ago
14

Suppose you have a Y-connected balanced three-phase load which consumes 200 kW with pf of 0.707 lagging. The line-to-line voltag

e of the load is 440 V. Use the line-to-line load voltage as your angle reference. (a) Draw the per-phase equivalent and label all the components. (b) Calculate the a-phase load current. (c) Calculate the capacitive reactive power per phase needed to correct the power factor to 0.8 lagging (d) Draw two power triangles - before and after the power factor correction in (c).

Engineering
1 answer:
elena55 [62]3 years ago
5 0

Given Information:

three-phase Y-connected load = P = 200 kW

PF = 0.707 lagging

line-to-line load voltage = VL-L = 440 V

Required Information:

(a) Draw the per-phase equivalent circuit ?

(b) Calculate the a-phase load current = ?

(c) Calculate the capacitive reactive power = ?

(d) Power triangles - before and after the power factor correction = ?

Answer:

a) See attached drawing  

b) I = 123.72<-45°

c) Qc = 16.66 kVAR

d) See attached drawing

Explanation:

b) Calculate the a-phase load current

VL-N = VL-L/\sqrt{3} = 440/\sqrt{3} = 254 V

Three phase load current can be found by

P = 3*VL-N*I*cos(θ)

θ = cos⁻¹(PF) = cos⁻¹(0.707) = 45°

I = P/3*VL-N*cos(45°)

I = 200,000/3*254*cos(45°)

I = 371.18 A

single phase current is

I = 371.18/3 = 123.72 A

In polar form,

I = 123.72<-45° A ( minus sign due to lagging PF)

Since the load is balanced, the current in other phases is same with 120° phase shift

(c) Calculate the capacitive reactive power

Three phase reactive compensation power is

Qc = P (tan(θold) - tan(θnew))

θnew = cos⁻¹(PF) = cos⁻¹(0.8) = 36.86°

Qc = 200 (tan(45°) - tan(36.86°))

Qc = 200 (0.250)

Qc = 50 kVAR

Per phase reactive compensation power is

Qc = 50/3 = 16.66 kVAR

(d) Power triangles - before and after the power factor correction

Before

P = 200 kW

Q =  3*VL-N*I*sin(45° ) = 3*254*123.72*sin(45° ) = 66.66 kVAR

S = P + jQ = 200 + j66.66 kVA = 210.81 kVA

After

I = P/3*VL-N*cos(36.86°) = 200,000/3*254*cos(36.86°) = 328 < -36.86 A

single phase current

I = 328/3 = 109.33 < -36.86 A

Q = 3*VL-N*I*sin(36.86° ) = 3*254*109.33*sin(36.86° ) = 50 kVAR

S = P + jQ = 200 + j50 kVA = 206 kVA

As you can see the current and reactive power are reduced after power factor correction.

The power triangle before and after power factor correction is attached.

You might be interested in
What is kinetic energy?
disa [49]

Answer:

kinetic energy means energy which a body possesses by virtue of being in motion

3 0
3 years ago
Read 2 more answers
Which of the following is most likely to require changes to existing zoning laws?
oksano4ka [1.4K]

Answer:

Adaptive reuse

thats it thankyou

8 0
2 years ago
Explain why veracity, value, and visualization can also be said to apply to relational databases as well as Big Data.
Hatshy [7]

Answer:

Veracity, Value and Visualization are not only the characteristics of Big Data but are also the characteristics of relational databases. Veracity of data is issue with smallest data stores this is the reason that it is important in relation...

5 0
3 years ago
The Accenture team is involved in helping a client in the transformation journey using Cloud computing. How is myNav beneficial
professor190 [17]

Answer:

It helps ensure the security of client data.

Explanation:

Cloud computing is one of the security features in networking which is being adopted by big corporations and organizations inorder to ensure smooth running of the organization.

Also, due to the sensitivity of data which some organizations deals in, they tried everything possible to protect themselves and their clients' information through use of cloud computing.<em> Data are stored in the clouds, and requires special administrative rights for it to be accessed by some of the staffs working in any given organization.</em>

8 0
3 years ago
A kernel-level thread wishes to acquire a mutex lock declared as global in the process. True or False: the function call used be
Alik [6]

Answer:

  1. A kernel-level thread wishes to acquire a mutex lock declared as global in the process.  <u>"</u><u>True"</u>  
  2. The function call used below causes the thread to block at this point, if the mutex lock is already acquired by a different thread. int resultcode -pthread mutex_trylock (myMutex). <u>"False"</u>                              

7 0
3 years ago
Other questions:
  • g The pump inlet is located 1 m above an arbitrary datum. The pressure and velocity at the inlet are 100 kPa and 2 m/s, respecti
    8·1 answer
  • As an employee, who's is supposed to provide training on the chemicals you are handling or come in contact with at work?
    14·2 answers
  • Why do conditional statements always have only two outcomes?
    8·1 answer
  • How much heat (Btu) is prod uced by a 150-W light bulb that is on for 20-hours?
    14·1 answer
  • What are the different branches of engineering involved in manufacturing a general-purpose elevator?
    6·1 answer
  • The products of combustion from a burner are routed to an industrial application through a thin-walled metallic duct of diameter
    11·1 answer
  • Complete the following sentence.
    10·1 answer
  • Imagine a cantilever beam fixed at one end with a mass = m and a length = L. If this beam is subject to an inertial force and a
    6·1 answer
  • What factors need to be considered when building housing on a waterway
    10·2 answers
  • who wants points for now work just put any answer who wants points for now work just put any answer who wants points for now wor
    5·1 answer
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!