Suppose you have a Y-connected balanced three-phase load which consumes 200 kW with pf of 0.707 lagging. The line-to-line voltag

e of the load is 440 V. Use the line-to-line load voltage as your angle reference. (a) Draw the per-phase equivalent and label all the components. (b) Calculate the a-phase load current. (c) Calculate the capacitive reactive power per phase needed to correct the power factor to 0.8 lagging (d) Draw two power triangles - before and after the power factor correction in (c).

Engineering
1 answer:
elena55 [62]3 years ago
5 0

Given Information:

three-phase Y-connected load = P = 200 kW

PF = 0.707 lagging

line-to-line load voltage = VL-L = 440 V

Required Information:

(a) Draw the per-phase equivalent circuit ?

(b) Calculate the a-phase load current = ?

(c) Calculate the capacitive reactive power = ?

(d) Power triangles - before and after the power factor correction = ?

Answer:

a) See attached drawing  

b) I = 123.72<-45°

c) Qc = 16.66 kVAR

d) See attached drawing

Explanation:

b) Calculate the a-phase load current

VL-N = VL-L/\sqrt{3} = 440/\sqrt{3} = 254 V

Three phase load current can be found by

P = 3*VL-N*I*cos(θ)

θ = cos⁻¹(PF) = cos⁻¹(0.707) = 45°

I = P/3*VL-N*cos(45°)

I = 200,000/3*254*cos(45°)

I = 371.18 A

single phase current is

I = 371.18/3 = 123.72 A

In polar form,

I = 123.72<-45° A ( minus sign due to lagging PF)

Since the load is balanced, the current in other phases is same with 120° phase shift

(c) Calculate the capacitive reactive power

Three phase reactive compensation power is

Qc = P (tan(θold) - tan(θnew))

θnew = cos⁻¹(PF) = cos⁻¹(0.8) = 36.86°

Qc = 200 (tan(45°) - tan(36.86°))

Qc = 200 (0.250)

Qc = 50 kVAR

Per phase reactive compensation power is

Qc = 50/3 = 16.66 kVAR

(d) Power triangles - before and after the power factor correction

Before

P = 200 kW

Q =  3*VL-N*I*sin(45° ) = 3*254*123.72*sin(45° ) = 66.66 kVAR

S = P + jQ = 200 + j66.66 kVA = 210.81 kVA

After

I = P/3*VL-N*cos(36.86°) = 200,000/3*254*cos(36.86°) = 328 < -36.86 A

single phase current

I = 328/3 = 109.33 < -36.86 A

Q = 3*VL-N*I*sin(36.86° ) = 3*254*109.33*sin(36.86° ) = 50 kVAR

S = P + jQ = 200 + j50 kVA = 206 kVA

As you can see the current and reactive power are reduced after power factor correction.

The power triangle before and after power factor correction is attached.

You might be interested in
Firefighters are holding a nozzle at the end of a hose while trying to extinguish a fire. The nozzle exit diameter is 8 cm, and
ivanzaharov [21]

Question

Determine the average water exit velocity

Answer:

53.05 m/s

Explanation:

Given information

Volume flow rate, Q=16 m^{3}/min

Diameter d= 8cm= 0.08 m

Assumptions

  • The flow is jet flow hence momentum-flux correction factor is unity
  • Gravitational force is not considered
  • The flow is steady, frictionless and incompressible
  • Water is discharged to the atmosphere hence pressure is ignored

We know that Q=AV and making v the subject then

V=\frac {Q}{A} where V is the exit velocity and A is area

Area, A=\frac {\pi d^{2}{4} where d is the diameter

By substitution

V=\frac {16\times 4}{\pi 0.08^{2}}=3183.098862 m/min

To convert v to m/s from m/s, we simply divide it by 60 hence

V=\frac {3183.098862  m/min}{60 s}=53.0516477 m/s\approx 53.05 m/s

3 0
3 years ago
section 10.1 describes a man in the middle attack on the diffie-hellman key exhange protocal in which the adversary generates tw
nika2105 [10]

Answer:

1. James will attack by generating a random private key XD and a corresponding public key YD.

2. Jane transmit YA to another person called Alex.

3. James intercept YA and transmit YD to jane.

4. Jane receive YD and calculate K1

At this point james and jane thinks they share a secret key but instead james has a secret key k1 to Jane and k2 to alex.

5. Alex transmit another key XA to alex for example.

6. James intercept and calculate k2 and vice versa.

6 0
3 years ago
A battery is an electromechanical device. a)- True b)- False
lilavasa [31]

Answer:

b)False

Explanation:

A battery is a device which store the energy in the form of chemical energy.And this stored energy is used according to the requirement.So battery is not a electromechanical device.Because it does have any mechanical component like gear ,shaft flywheel etc.

A flywheel is known as mechanical battery because it stored mechanical energy and supply that energy when more energy is required.Generally fly wheel is used during punching operation.

5 0
3 years ago
A 1020 CD steel shaft is to transmit 15 kW while rotating at 1750 rpm. Determine the minimum diameter for the shaft to provide a
vladimir2022 [97]

Answer:

diameter is 14 mm

Explanation:

given data

power = 15 kW

rotation N = 1750 rpm

factor of safety = 3

to find out

minimum diameter

solution

we will apply here power formula to find T that is

power = 2π×N×T / 60    .................1

put here value

15 ×10^{3} = 2π×1750×T / 60

so

T = 81.84 Nm

and

torsion = T / Z                        ..........2

here Z is section modulus i.e = πd³/ 16

so from equation 2

torsion = 81.84 / πd³/ 16

so torsion = 416.75 / / d³     .................3

so from shear stress theory

torsion = σy / factor of safety

so here σy = 530 for 1020 steel

so

torsion = σy / factor of safety

416.75 / d³ = 530 × 10^{6} / 3

so d = 0.0133 m

so diameter is 14 mm

3 0
3 years ago
An aluminum alloy tube with an outside diameter of 3.50 in. and a wall thickness of 0.30 in. is used as a 14 ft long column. Ass
slega [8]

Answer:

slenderness ratio = 147.8

buckling load = 13.62 kips

Explanation:

Given data:

outside diameter is 3.50 inc

wall thickness 0.30 inc

length of column is 14 ft

E = 10,000 ksi

moment of inertia = \frac{\pi}{64 (D_O^2 -D_i^2)}

I = \frac{\pi}{64}(3.5^2 -2.9^2) = 3.894 in^4

Area = \frac{\pi}{4} (3.5^2 -2.9^2) = 3.015 in^2

radius = \sqrt{\frac{I}{A}}

r = \sqrt{\frac{3.894}{3.015}

r = 1.136 in

slenderness ratio = \frac{L}{r}

                              = \frac{14 *12}{1.136} = 147.8

buckling load = P_cr = \frac{\pi^2 EI}}{l^2}

P_{cr} = \frac{\pi^2 *10,000*3.844}{( 14\times 12)^2}

P_{cr} = 13.62 kips

3 0
3 years ago
Other questions:
  • Yield and tensile strengths and modulus of elasticity . with increasing temperature. (increase/decrease/independent)
    11·1 answer
  • If the outside diameter of a pipe is 2 m, the length of a piece of insulation wrapped around it would be a)- 628 cm b)- 12.56 m.
    15·1 answer
  • Air at atmospheric pressure and at 300K flows with a velocity of 1.5m/s over a flat plate. The transition from laminar to turbul
    13·1 answer
  • 1. Using the formula above, complete this task.
    9·1 answer
  • if when you put your shirt in your pants, your shirt is tucked, does that mean when your shirt is over your pants, your pants ar
    6·2 answers
  • Think about the KIA factory shown in the video, what are two things that managers could do to reduce waste or increase efficienc
    6·1 answer
  • Find the value of L
    9·1 answer
  • Which band has an average of $3.58 per hour of parking?
    11·1 answer
  • Assume the availability of an existing class, ICalculator, that models an integer arithmetic calculator and contains: an instanc
    10·1 answer
  • Write a statement that calls the recursive method backwardsAlphabet() with parameter startingLetter.
    15·1 answer
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!