Complete Question
The complete question is shown on the first uploaded image 
Answer:
a
The High Voltage Rating for Auto - Transformer is 86kV
The  Low Voltage Rating for Auto - Transformer is 78kV
The MVA rating is 268.75
 b
The efficiency is 99.4% 
Explanation:
From the question  we are given are given that 
  The transformer has Mega Volt Amp rating of 25MVA
                           The frequency is 60-Hz 
                            Voltage rating 8.0kV : 78kV
    The short circuit test gives : 453kV,321A,77.5kW
    The open circuit test gives : 8.0kV, 39.6A, 86.2kW
This can be represented on a diagram shown on the second uploaded image 
From this diagram we can deduce that the The High Voltage Rating for Auto - Transformer is 86kV and the  Low Voltage Rating for Auto - Transformer is 78kV
  Now to obtain the current flowing through the 8kV  coil in the Auto-transformer we have 
              
The volt will cancel each other 
              
  Now to obtain the required MVA rating we would multiply the value of Power obtained during the open circuit test by the value of the current calculated.we are making use of the power obtain during open circuit testing because the transformer at this point is not under any load.
 
 We need to understand that Iron losses is due to open circuit test which has power = 86.2kW
While copper loss is due to short circuit test which has power = 77.5kW
The the current flowing through the secondary coil  as shown in the circuit diagram can be obtained as
 as shown in the circuit diagram can be obtained as 
        
Now the efficiency can be obtained as thus 
            
              =99.941%