Answer:
COP(heat pump) = 2.66
COP(Theoretical maximum) = 14.65
Explanation:
Given:
Q(h) = 200 KW
W = 75 KW
Temperature (T1) = 293 K
Temperature (T2) = 273 K
Find:
COP(heat pump)
COP(Theoretical maximum)
Computation:
COP(heat pump) = Q(h) / W
COP(heat pump) = 200 / 75
COP(heat pump) = 2.66
COP(Theoretical maximum) = T1 / (T1 - T2)
COP(Theoretical maximum) = 293 / (293 - 273)
COP(Theoretical maximum) = 293 / 20
COP(Theoretical maximum) = 14.65
Answer: