Answer:
1.3cm
Explanation:
the arrow is 3 lines past the 1 so it is 1.3cm
Answer:
It should be in Park or Neutral.
Explanation:
Answer:
it is not possible to place the wires in the condui
Explanation:
given data
total area = 2.04 square inches
wires total area = 0.93 square inches
maximum fill conduit = 40%
to find out
Can it is possible place wire in conduit conduit
solution
we know maximum fill is 40%
so here first we get total area of conduit that will be
total area of conduit = 40% × 2.04
total area of conduit = 0.816 square inches
but this area is less than required area of wire that is 0.93 square inches
so we can say it is not possible to place the wires in the conduit
Answer:
Tack coat is a sprayed application of an asphalt binder upon an existing asphalt or Portland cement concrete pavement prior to an overlay, or between layers of new asphalt concrete.
Explanation: