Answer:
Check the explanation
Explanation:
Question 1.
The secondary current of 250/5 amps CT when 300 amps(rated current of transmission line ) flow in TL is
(5/250 ) X 300 = 6 amps
Question 2
The correct answer to this second question is yes, when Over current relay coil will operate and relay contacts gets close, if the pickup value( Ip) of relay is set as 6 amps in relay. ( because primary current of TL is 1.2 times of CT primary)
Question 3
Tap Block figure (Fig 1) is not available/uploaded in your question.
Answer:

Explanation:
Soil bearing pressure=
Since we're given pressure of 2500 psf and load of 45000 pounds
The area=
Therefore, the smallest area of safe footings should not be less than 
Well, I do know that polarity affects the voltage.
Answer:
no
Explanation:
it's not a dead load because when load is put on the pillars it's not fully straining it's been slowly getting to be heavier in that period of time before it falls
Answer:
social regulation.
Explanation:
Social regulation are rules set aside to protect the environment or restrain activities that poses threat to public health and safety, examples includes environment pollution which includes lands, air, water etc, unhealthy work environment, etc. This rules identify activities that are allowed or under sanction for individuals, firms and government, breaking this rules most times comes with heavy fines or sanctions.