Answer:
a. 2.08, b. 1110 kJ/min
Explanation:
The power consumption and the cooling rate of an air conditioner are given. The COP or Coefficient of Performance and the rate of heat rejection are to be determined. <u>Assume that the air conditioner operates steadily.</u>
a. The coefficient of performance of the air conditioner (refrigerator) is determined from its definition, which is
COP(r) = Q(L)/W(net in), where Q(L) is the rate of heat removed and W(net in) is the work done to remove said heat
COP(r) = (750 kJ/min/6 kW) x (1 kW/60kJ/min) = 2.08
The COP of this air conditioner is 2.08.
b. The rate of heat discharged to the outside air is determined from the energy balance.
Q(H) = Q(L) + W(net in)
Q(H) = 750 kJ/min + 6 x 60 kJ/min = 1110 kJ/min
The rate of heat transfer to the outside air is 1110 kJ for every minute.
Answer:
hshdhriwjajaldh skshdjdywuusg
Explanation:
null
Answer:
4. A series of steps engineers use to solve problems.
Explanation:
The process of engineering design is a sequence of procedures that engineers pursue to arrive at a solution to a specific problem. Most times the solution includes creating a product such as a computer code, which fulfills certain conditions or performs a function. If the project in-hand includes designing, constructing, and testing it, then engineers probably adopt the design process. Steps of the process include defining the problem, doing background research, specifying requirements, brainstorming solutions, etc.