Answer:
a. 2.08, b. 1110 kJ/min
Explanation:
The power consumption and the cooling rate of an air conditioner are given. The COP or Coefficient of Performance and the rate of heat rejection are to be determined. <u>Assume that the air conditioner operates steadily.</u>
a. The coefficient of performance of the air conditioner (refrigerator) is determined from its definition, which is
COP(r) = Q(L)/W(net in), where Q(L) is the rate of heat removed and W(net in) is the work done to remove said heat
COP(r) = (750 kJ/min/6 kW) x (1 kW/60kJ/min) = 2.08
The COP of this air conditioner is 2.08.
b. The rate of heat discharged to the outside air is determined from the energy balance.
Q(H) = Q(L) + W(net in)
Q(H) = 750 kJ/min + 6 x 60 kJ/min = 1110 kJ/min
The rate of heat transfer to the outside air is 1110 kJ for every minute.
Answer:
a) 2622.903 N/m^3
b) 1.38233
c)4.878811765
Explanation:
Find the void ratio using the formula:

Here;
is specific gravity of soil solids
is unit weight of water = 998 kg/m^3
is the moisture content = 0.17
is the void ratio
is the unit weight of soil = 14.9KN/m^3
Saturation Ratio Formula:

S is saturation rate
Substitute Eq 2 into Eq 1


Specific gravity of soil solids

Saturated Unit Weight

Complete Question
Air at 40C flows over a 2 m long flat plate with a free stream velocity of 7m/s. Assume the width of the plate (into the paper) is 0.5 m. If the plate is at a co temperature of 100C,find:
The total heat transfer rate from the plate to the air
Answer:

Explanation:
From the question we are told that:
Air Temperature 
Length 
Velocity 
Width 
Constant temperature 
Generally the equation for Total heat Transfer is mathematically given by

Where
h=Convective heat transfer coefficient

Therefore




Answer:
<h2>hope it helps you see the attachment for further information .....✌✌✌✌✌</h2>
Answer: The energy system related to your question is missing attached below is the energy system.
answer:
a) Work done = Net heat transfer
Q1 - Q2 + Q + W = 0
b) rate of work input ( W ) = 6.88 kW
Explanation:
Assuming CPair = 1.005 KJ/Kg/K
<u>Write the First law balance around the system and rate of work input to the system</u>
First law balance ( thermodynamics ) :
Work done = Net heat transfer
Q1 - Q2 + Q + W = 0 ---- ( 1 )
rate of work input into the system
W = Q2 - Q1 - Q -------- ( 2 )
where : Q2 = mCp T = 1.65 * 1.005 * 293 = 485.86 Kw
Q2 = mCp T = 1.65 * 1.005 * 308 = 510.74 Kw
Q = 18 Kw
Insert values into equation 2 above
W = 6.88 Kw