Answer:
<em> - 14.943 W/m^2K ( negative sign indicates cooling ) </em>
Explanation:
Given data:
Area of FPC = 4 m^2
temp of water = 60°C
flow rate = 0.06 l/s
ambient temperature = 8°C
exit temperature = 49°C
<u>Calculate the overall heat loss coefficient </u>
Note : heat lost by water = heat loss through convection
m*Cp*dT = h*A * ( T - To )
∴ dT / T - To = h*A / m*Cp ( integrate the relation )
In (
) = h* 4 / ( 0.06 * 10^-3 * 1000 * 4180 )
In ( 41 / 52 ) = 0.0159*h
hence h = - 0.2376 / 0.0159
= - 14.943 W/m^2K ( heat loss coefficient )
Answer:
t = 6179.1 s = 102.9 min = 1.7 h
Explanation:
The energy provided by the resistance heater must be equal to the energy required to boil the water:
E = ΔQ
ηPt = mH
where.
η = efficiency = 84.5 % = 0.845
P = Power = 2.61 KW = 2610 W
t = time = ?
m = mass of water = 6.03 kg
H = Latent heat of vaporization of water = 2.26 x 10⁶ J/kg
Therefore,
(0.845)(2610 W)t = (6.03 kg)(2.26 x 10⁶ J/kg)
![t = \frac{1.362\ x\ 10^7\ J}{2205.45\ W}](https://tex.z-dn.net/?f=t%20%3D%20%5Cfrac%7B1.362%5C%20x%5C%2010%5E7%5C%20J%7D%7B2205.45%5C%20W%7D)
<u>t = 6179.1 s = 102.9 min = 1.7 h</u>
Answer:
a)Are generally associated with factor.
Explanation:
We know that losses are two types
1.Major loss :Due to friction of pipe surface
2.Minor loss :Due to change in the direction of flow
As we know that when any hindrance is produced during the flow of fluid then it leads to generate the energy losses.If flow is along uniform diameter pipe then there will not be any loss but if any valve and fitting placed is the path of fluid flow due to this direction of fluid flow changes and it produce losses in the energy.
Lot' of experimental data tell us that loss in the energy due to valve and fitting are generally associated with K factor.These losses are given as
![Losses=K\dfrac{V^2}{2g}](https://tex.z-dn.net/?f=Losses%3DK%5Cdfrac%7BV%5E2%7D%7B2g%7D)