The three phase full load secondary amperage is 2775.7 A
Explanation:
Following data is given,
S = Apparent Power = 1000 kVA
No. of phases = 3
Secondary Voltage: 208 V/120 V <em>(Here 208 V is three phase voltage and 120 V is single phase voltage) </em>
<em>Since,</em>
<em />
<em />
<em />

The formula for apparent power in three phase system is given as:

Where:
S = Apparent Power
V = Line Voltage
I = Line Current
In order to calculate the Current on Secondary Side, substituting values in above formula,

Answer:
See explaination
Explanation:
Please kindly check attachment for the step by step solution of the given problem.
Answer:
The principal stresses are σp1 = 27 ksi, σp2 = -37 ksi and the shear stress is zero
Explanation:
The expression for the maximum shear stress is given:

Where
σx = stress in vertical plane = 20 ksi
σy = stress in horizontal plane = -30 ksi
τM = 32 ksi
Replacing:

Solving for τxy:
τxy = ±19.98 ksi
The principal stress is:

Where
σp1 = 20 ksi
σp2 = -30 ksi
(equation 1)
equation 2
Solving both equations:
σp1 = 27 ksi
σp2 = -37 ksi
The shear stress on the vertical plane is zero
Explanation:
The end-use industries of thermochromic materials include packaging, printing & coating, medical, textile, industrial, and others. Printing & coating is the fastest-growing end-use industry of thermochromic materials owing to a significant increase in the demand for thermal paper for POS systems. The use of thermochromic materials is gaining momentum for interactive packaging that encourages consumers to take a product off the shelf and use it.