Answer:
it is not possible to place the wires in the condui
Explanation:
given data
total area = 2.04 square inches
wires total area = 0.93 square inches
maximum fill conduit = 40%
to find out
Can it is possible place wire in conduit conduit
solution
we know maximum fill is 40%
so here first we get total area of conduit that will be
total area of conduit = 40% × 2.04
total area of conduit = 0.816 square inches
but this area is less than required area of wire that is 0.93 square inches
so we can say it is not possible to place the wires in the conduit
Answer:
because burning rubber increases the grip power
Answer:
L = 475.718
T = 240.89 ft
M = 23.0195
LC = 472.728
R = 1225 ft
Explanation:
See the attached file for the calculation.
Answer:
Yes
Explanation:
Yes it is true that COP of heat pump always greater than 1.But the COP of refrigeration can be greater or less than 1.
We know that
COP of heat pump= 1 + COP of refrigeration
It is clear that COP can not be negative .So from the above expression we can say that COP of heat pump is always greater than one.
Answer:
Option D
All the above
Explanation:
Depending with the number of occupants in a building, the number of air conditioners required can either be increased or reduced. For instance, if the building is to be a classroom of over 50 students, 1 air-conditioner can't serve effectively. Similarly, the activity of occupants also dictate the amount of air conditioners required since if it's a gym room where occupants exercise often then the air conditioners required is different from if the room was to serve as a lounge. The appliances that also operate in a room require that air conditioners be installed as per the heat that may be generated by the appliances.