RideAnS [48]
3 years ago
12

2. A counter flow tube-shell heat exchanger is used to heat a cold water stream from 18 to 78oC at a flow rate of 1 kg/s. Heatin

g is provided by a superhot water stream in the shell at 160oC flowing at 1.8 kg/s. Inner tube diameter is 1.4 cm while the tube wall is very thin. Overall heat transfer coefficient based on the inner tube is 630 W/m2 K. Assume constant water properties in the cold stream; use values at 320K. The cp value for the hot stream is 4.30 kJ/kg K. (30%) a. Determine the length of the heat exchanger using the ε-NTU method; b. Estimate the cold side heat transfer coefficient.

Engineering
1 answer:
Anastaziya [24]3 years ago
5 0

Answer:

a) L = 220\,m, b) U_{o} \approx 0.63\,\frac{kW}{m^{2}\cdot ^{\textdegree}C}

Explanation:

a) The counterflow heat exchanger is presented in the attachment. Given that cold water is an uncompressible fluid, specific heat does not vary significantly with changes on temperature. Let assume that cold water has the following specific heat:

c_{p,c} = 4.186\,\frac{kJ}{kg\cdot ^{\textdegree}C}

The effectiveness of the counterflow heat exchanger as a function of the capacity ratio and NTU is:

\epsilon = \frac{1-e^{-NTU\cdot(1-c)}}{1-c\cdot e^{-NTU\cdot (1-c)}}

The capacity ratio is:

c = \frac{C_{min}}{C_{max}}

c = \frac{(1\,\frac{kg}{s} )\cdot(4.186\,\frac{kW}{kg^{\textdegree}C} )}{(1.8\,\frac{kg}{s} )\cdot(4.30\,\frac{kW}{kg^{\textdegree}C} )}

c = 0.541

Heat exchangers with NTU greater than 3 have enormous heat transfer surfaces and are not justified economically. Let consider that NTU = 2.5. The efectiveness of the heat exchanger is:

\epsilon = \frac{1-e^{-(2.5)\cdot(1-0.541)}}{1-(2.5)\cdot e^{-(2.5)\cdot (1-0.541)}}

\epsilon \approx 0.824

The real heat transfer rate is:

\dot Q = \epsilon \cdot \dot Q_{max}

\dot Q = \epsilon \cdot C_{min}\cdot (T_{h,in}-T_{c,in})

\dot Q = (0.824)\cdot (4.186\,\frac{kW}{^{\textdegree}C} )\cdot (160^{\textdegree}C-18^{\textdegree}C)

\dot Q = 489.795\,kW

The exit temperature of the hot fluid is:

\dot Q = \dot m_{h}\cdot c_{p,h}\cdot (T_{h,in}-T_{h,out})

T_{h,out} = T_{h,in} - \frac{\dot Q}{\dot m_{h}\cdot c_{p,h}}

T_{h,out} = 160^{\textdegree}C + \frac{489.795\,kW}{(7.74\,\frac{kW}{^{\textdegree}C} )}

T_{h,out} = 96.719^{\textdegree}C

The log mean temperature difference is determined herein:

\Delta T_{lm} = \frac{(T_{h,in}-T_{c, out})-(T_{h,out}-T_{c,in})}{\ln\frac{T_{h,in}-T_{c, out}}{T_{h,out}-T_{c,in}} }

\Delta T_{lm} = \frac{(160^{\textdegree}C-78^{\textdegree}C)-(96.719^{\textdegree}C-18^{\textdegree}C)}{\ln\frac{160^{\textdegree}C-78^{\textdegree}C}{96.719^{\textdegree}C-18^{\textdegree}C} }

\Delta T_{lm} \approx 80.348^{\textdegree}C

The heat transfer surface area is:

A_{i} = \frac{\dot Q}{U_{i}\cdot \Delta T_{lm}}

A_{i} = \frac{489.795\,kW}{(0.63\,\frac{kW}{m^{2}\cdot ^{\textdegree}C} )\cdot(80.348^{\textdegree}C) }

A_{i} = 9.676\,m^{2}

Length of a single pass counter flow heat exchanger is:

L =\frac{A_{i}}{\pi\cdot D_{i}}

L = \frac{9.676\,m^{2}}{\pi\cdot (0.014\,m)}

L = 220\,m

b) Given that tube wall is very thin, inner and outer heat transfer areas are similar and, consequently, the cold side heat transfer coefficient is approximately equal to the hot side heat transfer coefficient.

U_{o} \approx 0.63\,\frac{kW}{m^{2}\cdot ^{\textdegree}C}

You might be interested in
Can someone help me with this maze shown below.
Gnoma [55]
We can’t see the maze
3 0
3 years ago
Q2) An engineer borrowed $3000 from the bank, payable in six equal end-of-year payments at 8%. The bank agreed to reduce the int
tatyana61 [14]
Answer is: $637.28; just did the math but i really don’t want to type it all out.
6 0
3 years ago
A_____ transducer is a device that can convert an electronic controller output signal into a standard pneumatic output. A. pneum
makkiz [27]

Answer:

The correct answer is

option C. current to pneumatic (V/P)

Explanation:

A current to pneumatic controller is  basically used to receive an electronic signal from a controller and converts it further into a standard pneumatic output signal which is further used to operate a positioner or control valve. These devices are reliable, robust and accurate.

Though Voltage and current to pressure transducers are collectively called as electro pneumatic tranducers and the only electronic feature to control output pressure in them is the coil.

6 0
3 years ago
What is the volicity of a rocket?
Marysya12 [62]

Answer:

7.9 kilometers per second

Explanation:

8 0
3 years ago
Read 2 more answers
I am trying to test out the software Classroom relay and I am just ask if there is any way kids can stop Classroom relay form se
Inessa05 [86]

Answer:

What is classroom relay?

Plz answer in ch-at

Explanation:

3 0
3 years ago
Read 2 more answers
Other questions:
  • An old refrigerator consumes 247 W of power. Assuming that the refrigerator operates for 19 hours everyday, what is the annual o
    15·2 answers
  • Refrigerant-134a enters a diffuser steadily as saturated vapor at 600 kPa with a velocity of 160 m/s, and it leaves at 700 kPa a
    10·2 answers
  • Takt time is the rate at which a factory must produce to satisfy the customer's demand. a)- True b)- False
    11·1 answer
  • A stainless-steel specimen from the same material characterized up above, was formed into a rectangular cross-section of dimensi
    9·1 answer
  • A certain working substance receives 100 Btu reversibly as heat at a temperature of 1000℉ from an energy source at 3600°R. Refer
    13·1 answer
  • Basic output with variables (Java) This zyLab activity is intended for students to prepare for a larger programming assignment.
    7·1 answer
  • Hii I need help can someone help me
    15·1 answer
  • A bar of steel has the minimum properties Se = 40 kpsi, S = 60 kpsi, and S-80 kpsi. The bar is subjected to a steady torsional s
    6·1 answer
  • Q1. Basic calculation of the First law (2’) (a) Suppose that 150 kJ of work are used to compress a spring, and that 25 kJ of hea
    6·1 answer
  • Pay attention to the following questions!
    14·1 answer
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!