Question 1.
The secondary current of 250/5 amps CT when 300 amps(rated current of transmission line ) flow in TL is
(5/250 ) X 300 = 6 amps
Question 2
The correct answer to this second question is yes, when Over current relay coil will operate and relay contacts gets close, if the pickup value( Ip) of relay is set as 6 amps in relay. ( because primary current of TL is 1.2 times of CT primary)
Question 3
Tap Block figure (Fig 1) is not available/uploaded in your question.
Answer:
Explanation:
Mean temperature is given by

Tmean = (Ti + T∞)/2

Tmean = 107.5⁰C
Tmean = 107.5 + 273 = 380.5K
Properties of air at mean temperature
v = 24.2689 × 10⁻⁶m²/s
α = 35.024 × 10⁻⁶m²/s
= 221.6 × 10⁻⁷N.s/m²
= 0.0323 W/m.K
Cp = 1012 J/kg.K
Pr = v/α = 24.2689 × 10⁻⁶/35.024 × 10⁻⁶
= 0.693
Reynold's number, Re
Pv = 4m/πD²
where Re = (Pv * D)/
Substituting for Pv
Re = 4m/(πD
)
= (4 x 0.003)/( π × 6 ×10⁻³ × 221.6 × 10⁻⁷)
= 28728.3
Since Re > 2000, the flow is turbulent
For turbulent flows, Use
Dittus - Doeltr correlation with n = 0.03
Nu = 0.023Re⁰⁸Pr⁰³ = (h₁D)/k
(h₁ × 0.006)/0.0323 = 0.023(28728.3)⁰⁸(0.693)⁰³
(h₁ × 0.006)/0.0323 = 75.962
h₁ = (75.962 × 0.0323)/0.006
h₁ = 408.93 W/m².K