Answer:
a. 2.08, b. 1110 kJ/min
Explanation:
The power consumption and the cooling rate of an air conditioner are given. The COP or Coefficient of Performance and the rate of heat rejection are to be determined. <u>Assume that the air conditioner operates steadily.</u>
a. The coefficient of performance of the air conditioner (refrigerator) is determined from its definition, which is
COP(r) = Q(L)/W(net in), where Q(L) is the rate of heat removed and W(net in) is the work done to remove said heat
COP(r) = (750 kJ/min/6 kW) x (1 kW/60kJ/min) = 2.08
The COP of this air conditioner is 2.08.
b. The rate of heat discharged to the outside air is determined from the energy balance.
Q(H) = Q(L) + W(net in)
Q(H) = 750 kJ/min + 6 x 60 kJ/min = 1110 kJ/min
The rate of heat transfer to the outside air is 1110 kJ for every minute.
A question the design team should answer before handing off the designs is: are the designs a true representation of the intended end user experience?
<h3>What is a website?</h3>
A website can be defined as a collective name that is used to describe series of webpages that are interconnected or linked together with the same domain name.
In Computer technology, the main goal of a high-fidelity prototype is to understand how end users would interact with a website and areas to improve the design.
In conclusion, the design team should answer whether or not the designs are a true representation of the intended end user experience before handing off the designs.
Read more on website here: brainly.com/question/26324021
Answer:
Enthalpy at outlet=284.44 KJ
Explanation:


We need to Find enthalpy of outlet.
Lets take the outlet mass m and outlet enthalpy h.
So from mass conservation

m=1+1.5+2 Kg/s
m=4.5 Kg/s
Now from energy conservation

By putting the values

So h=284.44 KJ
Answer:

Explanation:
given data:
height of tank = 60cm
diameter of tank =40cm
accelration = 4 m/s2
suppose x- axis - direction of motion
z -axis - vertical direction
= water surface angle with horizontal surface
accelration in x direction
accelration in z direction
slope in xz plane is



the maximum height of water surface at mid of inclination is



the maximu height of wwater to avoid spilling is

= 60 - 8.2

the height requird if no spill water is 