The mass flow rate of cooling water required to cool the refrigerant is
.
Explanation:
A condenser is a heat exchanger used to cool working fluid (Refrigerant 134a) at the expense of cooling fluid (water), which works usually at steady state. Let suppose that there is no heat interactions between condenser and surroundings.The condenser is modelled after the First Law of Thermodynamics, which states:



The mass flow rate of the cooling water is now cleared:

Given that
,
,
and
, the mass flow of the cooling water is:


The mass flow rate of cooling water required to cool the refrigerant is
.
Answer:
The surface temperature of the ground is = 296.946K
Explanation:
Solution
Given
r₁= 0.05m
r₂= 0.08m
Tn =Ti = 77K
Ki = 0.0035 Wm-1K-1
Kg = 1 Wm-1K-1
Z= 2m
Now,
The outer type temperature (Skin temperature pipe)
Q = T₀ -T₁/ln (r2/r1)/2πKi = 2πKi T0 -T1/ln (r2/r1)
Thus,
10 w/m = 2π * 0.0035 = T0 -77/ln 0.08/0.05
⇒ T₀ -77 = 231.72
T₀= 290.72K
The shape factor between the cylinder and he ground
S = 2πL/ln 4z/D
where L = length of pipe
D = outer layer of pipe
S = 2π * 1/4 *2/ 2 * 0.08 = 1.606m
The heat gained in the pipe is = S * Kg * (Tg- T₀)
(10* 1) = 1.606 * 1* (Tg- 290.72)
Tg - 290.72 = 6.2266
Tg = 296.946K
Therefore the surface temperature to the ground is 296.946K