Total Resistance, Rt = (0.35 + 0.002 + 5200 + 0.5 + 0.008 + 1100) = 6300 ohms
a) Capacity of transformer, Pt = 150KVA = 150,000 W
Input Voltage, Vp = 2.8 KV = 2800 V
Current, Ip = 150000/2800 = 53.57 A
Input impedance, Zp = Vp/Ip = 2800/5357 = 52.27 ohms
b) i) Input current = 53.57 A
ii) Voltage, V = Ip * Rt = 53.57 X 6300 = 337.5 KV
iii) Power, P = I² * Rt = (53.57)² X 6300 = 18.08 MW
iv) Power factor = 0.83