Answer:
a) Ql=33120000 kJ
b) COP = 5.6
c) COPreversible= 29.3
Explanation:
a) of the attached figure we have:
HP is heat pump, W is the work supplied, Th is the higher temperature, Tl is the low temperature, Ql is heat supplied and Qh is the heat rejected. The worj is:
W=Qh-Ql
Ql=Qh-W
where W=2000 kWh
Qh=120000 kJ/h

b) The coefficient of performance is:

c) The coefficient of performance of a reversible heat pump is:

Th=20+273=293 K
Tl=10+273=283K
Replacing:

Answer:
it is not possible to place the wires in the condui
Explanation:
given data
total area = 2.04 square inches
wires total area = 0.93 square inches
maximum fill conduit = 40%
to find out
Can it is possible place wire in conduit conduit
solution
we know maximum fill is 40%
so here first we get total area of conduit that will be
total area of conduit = 40% × 2.04
total area of conduit = 0.816 square inches
but this area is less than required area of wire that is 0.93 square inches
so we can say it is not possible to place the wires in the conduit
One notable disadvantage of liquid cooling over air cooling is that it is considerably costly to set up. Cooling fans are prevalent in the market, and this overabundance of supply means they are cheap. The components of a liquid cooling system can be expensive.