Answer:
COP = 3.828
W' = 39.18 Kw
Explanation:
From the table A-11 i attached, we can find the entropy for the state 1 at -20°C.
h1 = 238.43 KJ/Kg
s1 = 0.94575 KJ/Kg.K
From table A-12 attached we can do the same for states 3 and 4 but just enthalpy at 800 KPa.
h3 = h4 = hf = 95.47 KJ/Kg
For state 2, we can calculate the enthalpy from table A-13 attached using interpolation at 800 KPa and the condition s2 = s1. We have;
h2 = 275.75 KJ/Kg
The power would be determined from the energy balance in state 1-2 where the mass flow rate will be expressed through the energy balance in state 4-1.
W' = m'(h2 - h1)
W' = Q'_L((h2 - h1)/(h1 - h4))
Where Q'_L = 150 kW
Plugging in the relevant values, we have;
W' = 150((275.75 - 238.43)/(238.43 - 95.47))
W' = 39.18 Kw
Formula foe COP is;
COP = Q'_L/W'
COP = 150/39.18
COP = 3.828
Answer:
1. Make sure the regulator adjustment screws are completely backed out and loose.
2. Open the main cylinder valves slowly.
3. Set the Oxygen and Acetylene working pressures.
4. Light and adjust the torch.
Explanation:
Answer:
UTP, STP, or fiber optic cable
Explanation:
The three cabling types are
1. UTP is unshielded twisted pair cables. It contains two unshielded wires that are wrapped around each other. Mostly used in telephone and LANs wires.
2. STP is shielded twisted pair. This can be compared to UTP but each if the pair has an extra copper braid jacket protecting it. It is used mainly for ethernet networks.
3. Fibre optics cables. These are network cables with strands iv glass fibers that are in an insulated casing.
This kind of cable can provide greater bandwidth as well as data transmission that goes over a long distance.