Answer:
1) 1.4(D + F)
2) 1.2(D + F + T) + 1.6(L + H) + 0.5(Lr or S or R)
3) 1.2D + 1.6(Lr or S or R) + ((0.5 or 1.0)*L or 0.8W)
4) 1.2D + 1.6W + (0.5 or 1.0)*L + 0.5(Lr or S or R)
5) 1.2D + 1.0E + (0.5 or 1.0)*L + 0.2S
6) 0.9D + 1.6W + 1.6H
7) 0.9D + 1.0E + 1.6H
Explanation:
Load and Resistance Factor Design
there are 7 basic load combination of LRFD that is
1) 1.4(D + F)
2) 1.2(D + F + T) + 1.6(L + H) + 0.5(Lr or S or R)
3) 1.2D + 1.6(Lr or S or R) + ((0.5 or 1.0)*L or 0.8W)
4) 1.2D + 1.6W + (0.5 or 1.0)*L + 0.5(Lr or S or R)
5) 1.2D + 1.0E + (0.5 or 1.0)*L + 0.2S
6) 0.9D + 1.6W + 1.6H
7) 0.9D + 1.0E + 1.6H
and
here load factor for L given ( * ) mean it is permitted = 0.5 for occupancies when live load is less than or equal to 100 psf
here
D is dead load and L is live load
E is earth quake load and S is snow load
W is wind load and R is rain load
Lr is roof live load
I attached a photo that explains and gives the answer to your questions. Had to add a border because the whole picture didn’t fit.
The two ways you can use to make an informal survey are:
- make field observations
- interview people using informal unstructured techniques
<h3>What are informal surveys?</h3>
In informal surveys can be regarded as a type of survey that can be made by the researcher by going to the field themselves and this can be done by using different methods or ways.
For instance, the researcher can go out to interview people that can give the data that is needed about the research such as informally asking them questions, unstructured techniques can also be used to solve critical issues.
learn more about survey at: brainly.com/question/6947486
#SPJ9
Answer:
critical clearing angle = 70.3°
Explanation:
Generator operating at = 50 Hz
power delivered = 1 pu
power transferable when there is a fault = 0.5 pu
power transferable before there is a fault = 2.0 pu
power transferable after fault clearance = 1.5 pu
using equal area criterion to determine the critical clearing angle
Attached is the power angle curve diagram and the remaining part of the solution.
The power angle curve is given as
= Pmax sinβ
therefore : 2sinβo = Pm
2sinβo = 1
sinβo = 0.5 pu
βo =
⁰
also ; 1.5sinβ1 = 1
sinβ1 = 1/1.5
β1 =
= 41.81⁰
∴ βmax = 180 - 41.81 = 138.19⁰
attached is the remaining solution
The critical clearing angle =
≈ 70.3⁰