11–17 A long, thin-walled double-pipe heat exchanger with tube and shell diameters of 1.0 cm and 2.5 cm, respectively, is used t

o condense refrigerant-134a with water at 20°C. The refrigerant flows through the tube, with a convection heat transfer coefficient of hi = 4100 W/m2·K. Water flows through the shell at a rate of 0.3 kg/s. Determine the overall heat transfer coefficient of this heat exchanger.
Engineering
1 answer:
lana [24]3 years ago
5 0

Answer:

the overall heat transfer coefficient of this heat exchanger is 1855.8923 W/m²°C

Explanation:

Given:

d₁ = diameter of the tube = 1 cm = 0.01 m

d₂ = diameter of the shell = 2.5 cm = 0.025 m

Refrigerant-134a

20°C is the temperature of water

h₁ = convection heat transfer coefficient = 4100 W/m² K

Water flows at a rate of 0.3 kg/s

Question: Determine the overall heat transfer coefficient of this heat exchanger, Q = ?

First at all, you need to get the properties of water at 20°C in tables:

k = 0.598 W/m°C

v = 1.004x10⁻⁶m²/s

Pr = 7.01

ρ = 998 kg/m³

Now, you need to calculate the velocity of the water that flows through the shell:

v_{w} =\frac{m}{\rho \pi (\frac{d_{2}^{2}-d_{1}^{2}  }{4} )} =\frac{0.3}{998*\pi (\frac{0.025^{2}-0.01^{2}  }{4}) } =0.729m/s

It is necessary to get the Reynold's number:

Re=\frac{v_{w}(d_{2}-d_{1}) }{v} =\frac{0.729*(0.025-0.01)}{1.004x10^{-6} } =10891.4343

Like the Reynold's number is greater than 10000, the regime is turbulent. Now, the Nusselt's number:

Nu=0.023Re^{0.8} Pr^{0.4} =0.023*(10891.4343)^{0.8} *(7.01)^{0.4} =85.0517

The overall heat transfer coefficient:

Q=\frac{1}{\frac{1}{h_{1} }+\frac{1}{h_{2} }  }

Here

h_{2} =\frac{kNu}{d_{2}-d_{1}} =\frac{0.598*85.0517}{0.025-0.01} =3390.7278W/m^{2}C

Substituting values:

Q=\frac{1}{\frac{1}{4100}+\frac{1}{3390.7278}  } =1855.8923W/m^{2} C

You might be interested in
Worth 20 points! Please help ASAP!
gulaghasi [49]

Answer:

I am in 6th grade, why are high school things popping up??

Explanation:

8 0
3 years ago
The bulk modulus of a material is 3.5 ✕ 1011 N/m2. What percent fractional change in volume does a piece of this material underg
kiruha [24]

Answer:

percentage change in volume  = 0.00285 %

Explanation:

given data

bulk modulus = 3.5 × 10^{11}  N/m²

bulk stress = 10^{7}  N/m²

solution

we will apply here bulk modulus formula that is

bulk modulus = \frac{bulk\ stress}{bulk\ strain}   ...............1

put here value and we get

3.5 × 10^{11} = \frac{10^7}{bulk\ strain}  

solve it we get

bulk strain = 2.8571 × 10^{-5}

and

bulk strain = \frac{change\ volume}{original\ volume}  

so that percentage change in volume is = 2.8571 × 10^{-5}  × 100

percentage change in volume  = 0.00285 %

6 0
3 years ago
What was the first roblox player A.bob B.roblox C.builderman
san4es73 [151]
Builderman is dksbdkbsnsbs
5 0
3 years ago
Read 2 more answers
Consider tests of an unswept wing that spans the wind tunnel and whose airfoil section is NACA 23012. Since the wing model spans
Dominik [7]

Answer:

Check the explanation

Explanation:

to know the lift per unit span (N/m) that is expected to be measured when the wing attack angle is 4°

as well as the corresponding section lift coefficient and die moment coefficient .

Kindly check the attached image below to see the step by step explanation to the above question.

3 0
3 years ago
A cooling system load is 96,000 BTUh sensible. How much chilled air is required to satisfy the load if the system is designed fo
Natalija [7]

Answer:

For 20^{\circ} - 5.556 lb/s

For 15^{\circ} - 7.4047 lb/s

Solution:

As per the question:

System Load = 96000 Btuh

Temperature, T = 20^{\circ}

Temperature rise, T' = 15^{\circ}

Now,

The system load is taken to be at constant pressure, then:

Specific heat of air, C_{p} = 0.24 btu/lb ^{\circ}F

Now, for a rise of 20^{\circ} in temeprature:

\dot{m}C_{p}\Delta T = 96000

\dot{m} = \frac{96000}{C_{p}\Delta T} = \frac{96000}{0.24\times 20} = 20000 lb/h = \frac{20000}{3600} = 5.556 lb/s

Now, for 15^{\circ}:

\dot{m}C_{p}\Delta T = 96000

\dot{m} = \frac{96000}{C_{p}\Delta T} = \frac{96000}{0.24\times 15} = 26666.667 lb/h = \frac{26666.667}{3600} = 7.4074 lb/s

4 0
2 years ago
Other questions:
  • "A computer architect redesigns the pipeline above to enable branch prediction. When PCSrc is asserted (branch taken) IF/ID is f
    10·1 answer
  • A common rule of thumb for controller discretization is to have "6 samples per rise time" in order to achieve a reasonable appro
    9·1 answer
  • A torsion member has an elliptical cross section with major and minor dimensions of 50.0 mm and 30.0 mm, respectively. The yield
    10·1 answer
  • Convection ovens operate on the principle of inducing forced convection inside the oven chamber with a fan. A small cake is to b
    6·1 answer
  • 5
    15·1 answer
  • A civil engineer is analyzing the compressive strength of concrete. The compressive strength is approximately normal distributed
    7·1 answer
  • Imagine waking up every day and no one is home besides your dog and you how would you feel?
    12·2 answers
  • Connecting rods undergo a process to alleviate manufacturing stresses from forging, a process known as ______.​
    7·1 answer
  • For a nozzle-duct system shown in Fig Q3, the nozzle is designed to produce a Mach number of 2.8 with y = 1.4, The inlet conditi
    14·1 answer
  • I know this answer i just want too see if people know it too
    9·2 answers
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!