Answer:
h_f = 15 ft, so option A is correct
Explanation:
The formula for head loss is given by;
h_f = [10.44•L•Q^(1.85)]/(C^(1.85))•D^(4.8655))
Where;
h_f is head loss due to friction in ft
L is length of pipe in ft
Q is flow rate of water in gpm
C is hazen Williams constant
D is diameter of pipe in inches
We are given;
L = 1,800 ft
Q = 600 gpm
C = 120
D = 8 inches
So, plugging in these values into the equation, we have;
h_f = [10.44*1800*600^(1.85)]/(120^(1.85))*8^(4.8655))
h_f = 14.896 ft.
So, h_f is approximately 15 ft
load every electric circuit,regardless of where it is or how large or small, has four basic parts: an energy source (ac or dc),a conductor (wire), an electrical load (device), and at least one controller(switch)
Answer:
D
Explanation:
To know which is most or least cost-effective, it's not enough to look at only the per day rate, or only the time to complete. You have to multiply them to get the total cost of the project.
![\left[\begin{array}{ccccc}&Cost\ per\ day\ (\$)&Time\ to\ complete\ (days)&Total\ cost\ (\$)\\Zoe&500&8&4000\\Greg&650&10&6500\\Orion&400&12&4800\\Jin&700&5&3500\end{array}\right]](https://tex.z-dn.net/?f=%5Cleft%5B%5Cbegin%7Barray%7D%7Bccccc%7D%26Cost%5C%20per%5C%20day%5C%20%28%5C%24%29%26Time%5C%20to%5C%20complete%5C%20%28days%29%26Total%5C%20cost%5C%20%28%5C%24%29%5C%5CZoe%26500%268%264000%5C%5CGreg%26650%2610%266500%5C%5COrion%26400%2612%264800%5C%5CJin%26700%265%263500%5Cend%7Barray%7D%5Cright%5D)
As you can see, Greg is the least cost-effective because he charges the most for the project.
Answer:
Explanation:
A smaller clearance volume means a higher compression. A higher compression means better thermal efficiency. However a compression ratio too high might be troublesome, as it can cause accidental ignition of the fuel-air mix. This is the reason why Otto cycle engines have lower compressions that Diesel engines. In a Diesel engine the mix ignites by compression instead of a spark.