Answer:
The three phase full load secondary amperage is 2775.7 A
Explanation:
Following data is given,
S = Apparent Power = 1000 kVA
No. of phases = 3
Secondary Voltage: 208 V/120 V <em>(Here 208 V is three phase voltage and 120 V is single phase voltage) </em>
<em>Since,</em>
<em />
<em />
<em />

The formula for apparent power in three phase system is given as:

Where:
S = Apparent Power
V = Line Voltage
I = Line Current
In order to calculate the Current on Secondary Side, substituting values in above formula,

Answer:
the hurts my brain sorry bud cant help
Explanation:
Answer:
The answer is copying a program to give to someone else to use
and burning a copy of a DVD to sell
Explanation:
Software piracy is the act of stealing software that is legally protected. This stealing includes copying, distributing, modifying or selling
Answer:
the minimum shaft diameter is 35.026 mm
the maximum shaft diameter is 35.042mm
Explanation:
Given data;
D-maximum = 35.020mm and d-minimum = 35.000mm
we have to go through Tables "Descriptions of preferred Fits using the Basic Hole System" so from the table, locational interference fits H7/p6
so From table, Selection of International Trade Grades metric series
the grade tolerance are;
ΔD = IT7(0.025 mm)
Δd = IT6(0.016 mm)
Also from Table "Fundamental Deviations for Shafts" metric series
Sf = 0.026
so
D-maximum
Dmax = d + Sf + Δd
we substitute
Dmax = 35 + 0.026 + 0.016
Dmax = 35.042 mm
therefore the maximum diameter of shaft is 35.042mm
d-minimum
Dmin = d + Sf
Dmin = 35 + 0.026
Dmin = 35.026 mm
therefore the minimum diameter of shaft is 35.026 mm