C. Both; require a wheel alignment after replacement
Answer:
a. 2.08, b. 1110 kJ/min
Explanation:
The power consumption and the cooling rate of an air conditioner are given. The COP or Coefficient of Performance and the rate of heat rejection are to be determined. <u>Assume that the air conditioner operates steadily.</u>
a. The coefficient of performance of the air conditioner (refrigerator) is determined from its definition, which is
COP(r) = Q(L)/W(net in), where Q(L) is the rate of heat removed and W(net in) is the work done to remove said heat
COP(r) = (750 kJ/min/6 kW) x (1 kW/60kJ/min) = 2.08
The COP of this air conditioner is 2.08.
b. The rate of heat discharged to the outside air is determined from the energy balance.
Q(H) = Q(L) + W(net in)
Q(H) = 750 kJ/min + 6 x 60 kJ/min = 1110 kJ/min
The rate of heat transfer to the outside air is 1110 kJ for every minute.
Answer:
M_c = 61.6 Nm
Explanation:
Given:
F_a = 2.5 KN
Find:
Determine the moment of this force about C for the two casesshown.
Solution:
- Draw horizontal and vertical vectors at point A.
- Take moments about point C as follows:
M_c = F_a*( 42 / 150 ) *88
M_c = 2.5*( 42 / 150 ) *88
M_c = 61.6 Nm
- We see that the vertical component of force at point A passes through C.
Hence, its moment about C is zero.
Answer:
It has poor tensile strength despite having high compressive strength
Explanation:
Concrete exhibits high compressive strength when used. However, it has very low compressive strength. This is the reason why concrete is normally combined with steel to make a composite building material called reinforced concrete. The steel reinforces concrete hence increasing the tensile strength in RC buildings. The end composite is durable and fireproof. Generally, the main reason why concrete is not use on its own is due to its poor tensile strength.