Answer:
Check the explanation
Explanation:
Question 1.
The secondary current of 250/5 amps CT when 300 amps(rated current of transmission line ) flow in TL is
(5/250 ) X 300 = 6 amps
Question 2
The correct answer to this second question is yes, when Over current relay coil will operate and relay contacts gets close, if the pickup value( Ip) of relay is set as 6 amps in relay. ( because primary current of TL is 1.2 times of CT primary)
Question 3
Tap Block figure (Fig 1) is not available/uploaded in your question.
Answer:
Check the attached image below
Explanation:
Kindly check the attached image below to get the step by step explanation to the question above.