Two loads connected in parallel draw a total of 2.4 kW at 0.8 pf lagging from a 120-V rms, 60-Hz line. One load absorbs 1.5 kW a

t a 0.707 pf lagging. Determine:
(a) the pf of the second load,
(b) the parallel element required to correct the pf to 0.9 lagging for the two loads.
Engineering
1 answer:
stealth61 [152]3 years ago
7 0

Answer: a) 0.948 b) 117.5µf

Explanation:

Given the load, a total of 2.4kw and 0.8pf

V= 120V, 60 Hz

P= 2.4 kw, cos θ= 80

P= S sin θ - (p/cos θ) sin θ

= P tan θ(cos^-1 (0.8)

=2.4 tan(36.87)= 1.8KVAR

S= 2.4 + j1. 8KVA

1 load absorbs 1.5 kW at 0.707 pf lagging

P= 1.5 kW, cos θ= 0.707 and θ=45 degree

Q= Ptan θ= tan 45°

Q=P=1.5kw

S1= 1.5 +1.5j KVA

S1 + S2= S

2.4+j1.8= 1.5+1.5j + S2

S2= 0.9 + 0.3j KVA

S2= 0.949= 18.43 °

Pf= cos(18.43°) = 0.948

b.) pf to 0.9, a capacitor is needed.

Pf = 0.9

Cos θ= 0.9

θ= 25.84 °

(WC) V^2= P (tan θ1 - tan θ2)

C= 2400 ( tan (36. 87°) - tan (25.84°)) /2 πf × 120^2

f=60, π=22/7

C= 117.5µf

You might be interested in
What is bubble sort?what is bubble sort ​
juin [17]

Answer:

Bubble sort, sometimes referred to as sinking sort, is a simple sorting algorithm that repeatedly steps through the list, compares adjacent elements and swaps them if they are in the wrong order. The pass through the list is repeated until the list is sorted.

Explanation:

Look at the photo

Good luck

4 0
3 years ago
Read 2 more answers
Hỗ trợ mình với được không các bạn
Leya [2.2K]

Answer:

Explanation:

Be bop

6 0
3 years ago
The beam is supported by a pin at A and a roller at B which has negligible weight and a radius of 15 mm. If the coefficient of s
Anettt [7]

Answer:

33.4

Explanation:

Step 1:

\sumMo=0 (moment about the origin)

Fb(15)-Fc(15)=0

Fb=Fc

Step 2:

\sumFx=0

-Fb-Fccos\theta+Ncsin\theta=0

Fc=0.3Nc=Fb

-0.3Nc-0.3Nccos\theta+Ncsin\theta=0

(-0.3-cos\theta+sin\theta)Nc=0----(1)

\sumFy=0

Nccos\theta+Fcsin\theta-Nb=0

Nccos\theta+0.3Ncsin\theta-Nc=0

Nc[cos\theta+0.3sin\theta-1]=0--------(2)

Solving eq (1) and eq (2)

\theta=33.4

Step 3:

As the roller is a two force member

2(90-\phi)+\theta=180

\phi=\theta/2

\phi=Tan(\muN/N)-1

\phi=16.7

\theta=2x16.7=33.4

5 0
3 years ago
A piston-cylinder device contains 0.1 m3 of liquid water and 0.9 m² of water vapor in equilibrium at 800 kPa. Heat is transferre
docker41 [41]

Answer:

Initial temperature = 170. 414 °C

Total mass = 94.478 Kg

Final volumen = 33.1181 m^3

Diagram  = see picture.

Explanation:

We can consider this system as a close system, because there is not information about any output or input of water, so the mass in the system is constant.  

The information tells us that the system is in equilibrium with two phases: liquid and steam. When a system is a two phases region (equilibrium) the temperature and pressure keep constant until the change is completed (either condensation or evaporation). Since we know that we are in a two-phase region and we know the pressure of the system, we can check the thermodynamics tables to know the temperature, because there is a unique temperature in which with this pressure (800 kPa) the system can be in two-phases region (reach the equilibrium condition).  

For water in equilibrium at 800 kPa the temperature of saturation is 170.414 °C which is the initial temperature of the system.  

to calculate the total mass of the system, we need to estimate the mass of steam and liquid water and add them. To get these values we use the specific volume for both, liquid and steam for the initial condition. We can get them from the thermodynamics tables.

For the condition of 800 kPa and 170.414 °C using the thermodynamics tables we get:

Vg (Specific Volume of Saturated Steam) = 0.240328 m^3/kg

Vf (Specific Volume of Saturated Liquid) = 0.00111479 m^3/kg

if you divide the volume of liquid and steam provided in the statement by the specific volume of saturated liquid and steam, we can obtain the value of mass of vapor and liquid in the system.

Steam mass = *0.9 m^3 / 0.240328 m^3/kg = 3.74488 Kg

Liquid mass = 0.1 m^3 /0.00111479 m^3/kg = 89.70299 Kg  

Total mass of the system = 3.74488 Kg + 89.70299 Kg = 93,4478 Kg

If we keep the pressure constant increasing the temperature the system will experience a phase-change (see the diagram) going from two-phase region to superheated steam. When we check for properties for the condition of P= 800 kPa and T= 350°C we see that is in the region of superheated steam, so we don’t have liquid water in this condition.  

If we want to get the final volume of the water (steam) in the system, we need to get the specific volume for this condition from the thermodynamics tables.  

Specific Volume of Superheated Steam at 800 kPa and 350°C = 0.354411 m^3/kg

We already know that this a close system so the mass in it keeps constant during the process.

 

If we multiply the mass of the system by the specific volume in the final condition, we can get the final volume for the system.  

Final volume = 93.4478 Kg * 0.354411 m^3/kg = 33.1189 m^3

You can the P-v diagram for this system in the picture.  

For the initial condition you can calculate the quality of the steam (measure of the proportion of steam on the mixture) to see how far the point is from for the condition on all the mix is steam. Is a value between 0 and 1, where 0 is saturated liquid and 1 is saturated steam.  

Quality of steam = mass of steam / total mass of the system

Quality of steam = 3.74488 Kg /93.4478 Kg = 0,040 this value is usually present as a percentage so is 4%.  

Since this a low value we can say that we are very close the saturated liquid point in the diagram.  

6 0
4 years ago
The minimum fresh air requirement of a residential building is specified to be 0.35 air changes per hour (ASHRAE, Standard 62, 1
Thepotemich [5.8K]

Answer:

a) The flow capacity of the fan is 3150 L/min

d) the minimum diameter is 0.11 m

Explanation:

given data:

A = area of residence = 200 m²

h = height of building = 2.7 m

Percentage of air that must be replaced by fresh air is 35%

v = velocity of air in the duct = 5.5 m/s

a) The volume of the entire building is:

Volume=2.7*200=540m^{3}

The flow capacity of the fan is equal to:

Flow=\frac{0.35*540}{60} =3.15m^{3} /min

Flow=3.15\frac{m^{3} }{min} *\frac{1000L}{1m^{3}  } =3150L/min

b) The volume flow rate of fresh air is equal to:

Flow=\frac{\pi *d^{2} }{4} V\\d=\sqrt{\frac{4*Flow}{\pi V} } =\sqrt{\frac{4*3.15}{\pi *5.5*60} } =0.11m

6 0
4 years ago
Other questions:
  • Biologists use a sequence of letters A, C, T, and G to model a genome. A gene isa substring of a genome that starts after a trip
    5·1 answer
  • A fruit juice is being heated in an indirect heat exchanger using steam as a heating medium. The product flows through the heat
    12·1 answer
  • What is the capacity of the machine in batches?
    10·1 answer
  • A closed system undergoes an adiabatic process during which the work transfer into the system is 12 kJ. The system then returns
    14·1 answer
  • 1. An air standard cycle is executed within a closed piston-cylinder system and consists of three processes as follows:1-2 = con
    5·1 answer
  • Find the Hooke's law of orthotropic and transverse isotropic material in matrix form
    15·1 answer
  • Ray L. Zapp is thinking about testing strategies for his new HashTable class, which uses Rainforest's cloud storage service to m
    9·1 answer
  • 13. The members installed vertically over and under a window opening are called
    9·1 answer
  • Why might there be multiple foremen on one work site?
    11·1 answer
  • 4. When the ESC system senses oversteer,
    13·1 answer
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!