Answer:
There is 0.466 KW required to operate this air-conditioning system
Explanation:
<u>Step 1:</u> Data given
Heat transfer rate of the house = Ql = 755 kJ/min
House temperature = Th = 24°C = 24 +273 = 297 Kelvin
Outdoor temperature = To = 35 °C = 35 + 273 = 308 Kelvin
<u>Step 2: </u> Calculate the coefficient of performance o reversed carnot air-conditioner working between the specified temperature limits.
COPr,c = 1 / ((To/Th) - 1)
COPr,c = 1 /(( 308/297) - 1)
COPr,c = 1/ 0.037
COPr,c = 27
<u>Step 3:</u> The power input cna be given as followed:
Wnet,in = Ql / COPr,max
Wnet, in = 755 / 27
Wnet,in = 27.963 kJ/min
Win = 27.963 * 1 KW/60kJ/min = 0.466 KW
There is 0.466 KW required to operate this air-conditioning system
Answer:
Racking is the term used for when buildings tilt as their structural components are forced out of plumb. This is most commonly caused by wind forces exerting horizontal pressure, but it can also be caused by seismic stress, thermal expansion or contraction, and so on.
Explanation:
Answer: hope it helps
Explanation:Moving air has a force that will lift kites and balloons up and down. Air is a mixture ... Here is a simple computer simulation that you can use to explore how wings make lift. ... All these dimensions together combine to control the flight of the plane. A pilot ... When the rudder is turned to one side, the airplane moves left or right.
Answer:
hello your question has a missing part below is the missing part
Consider the string length equal to 
answer : 2cos(2t) sin(2x) - 10cos(10t)sin(10x)
Explanation:
Given string length =
distorted function f(x) = 2sin(2x) - 10sin(10x)
Determine the wave formed in the string
attached below is a detailed solution of the problem